steam radiator problem
dave_47
dave_47 Member Posts: 6
I have six steam radiators in my house. Only the top half of each radiator heats while the lower half stays cold. Does anyone have any ideas as to what the problem might be?
Thanks, Dave
  • Travis G.
    Travis G. Member Posts: 22
    pipe
    is this a 1 pipe or a 2 pipe steam system? Is this your first time haveing steam as your heat?
  • Dale
    Dale Member Posts: 1,317
    Boiler
    Did this just start? Does the stat turn the boiler off when the rads get 1/2 hot or does the burner keep running to cut out pressure? My guess so far is that you need more main venting, I think the air isn't getting out fast enough. The 1/2 even part is actually good because it narrows the possibilites.
  • dave_47
    This is a one pipe system. The furnace is a Weil Mclean and is running at 84% efficiency.
  • dave_47
    Just noticed it this recently. The burner seems to cut on and off again fairly frequently.
  • JM_2
    JM_2 Member Posts: 108
    I you sure its steam
    I had a forced hoy water sys that did this.
    Steamhead Member Posts: 18,217
    Dave, are the vents
    mounted low on the side of the radiator, or at the top? If the latter, steam is rising to the top of the radiators and shutting the vents.
    Consulting