For a cooling requirement of 48,000 btus, what size (TONS?)unit would be required. Mad Dog
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=210&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=210&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
a/c tonnage
48,000 btus = 4 tons of coolong 12,000 btus = 1 ton of cooling
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
A ton of cooling is roughly equivalent to 12,000 btu/hr. It's based on the cooling power of a ton of ice--literally.0 -
What service !!!!!!!!!!!!!!!!!!!!
this wall is unbelievable. Thanks ED
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Really??? I love those old formulae!!!!!!!!!!
thanks Mike......md
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
If the source(s) I've read are correct, it's based on a one-ton (US ton I believe) block of ice in the middle of a room.0 -
Found a better definition
"One ton of refrigeration can get rid of the amount of heat that is needed to melt one short ton of ice in only 24 hours."0 -
a/c
you are welcome mad dog the other guys sid it better than i did
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Don't forget
Don't forget to allow for 400 cfm/ton of cooling or in this case, that 4 ton unit needs to move 1600 cfm of air flow. The supply and return duct are large when dealing with 4 & 5 ton units. If the building has a high latent heat load, the cfm can be reduced to 350 cfm/ton. to remove moisture and longer run times. Good idea to place a freeze stat on the coil or suction line to prevent coil icing. There is less margin for dirty air filters, unused rooms and cool outside air temperatures. A high sensible heat load set the fan to deliver more air flow, 450 cfm/ton.
WD0 -
ton not necessarily 12kbtu
A nominal 4ton concensor will deliver different btus with different coils.
The ARI ratings are a good source of info.
You need to determine latent and sensible heat loads, then find a condensor/coil combo that matches those values.
Mark0 -
latent
and sensible combined MD?
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements