Electrical circuit for oil burner
Hello. I have a forced air oil furnace on a dedicated 15 amp circuit. The breaker has never tripped but I was curious about whether the circuit should be upgraded to 20 amp. Are most of these circuits 15 or 20 amp in new installations? Thanks and a happy Easter to all.
  • ed wallace
    ed wallace Member Posts: 1,612
    electric circuit
    oil burner systems are designed to run on 15 amp circuits leave it alone if if its working ok if its tripping you have an electrical problem
  • Bill NTSG
    Bill NTSG Member Posts: 321
    It depends
    On the wire size. #14 awg is only rated for 15amps. #12awg wire is good for 20 amp. #10awg wire = 30 amps. So if you have #14 wire and you install a 20 amp breaker or fuse you are exceeding the capacity of the wire.
    The only time you may need the 20 amp on a furnace is if you have a BIG blower with a 3/4 or 1 horse power motor.
  • Glenn Harrison
    Glenn Harrison Member Posts: 405
    Look at the nameplate in the furnace,
    it almost always has listed a minimum amps used and a maximum amps needed for the furnace. I personally have yet to see a residential gas or oil furnace that would need more than 15 amps, and a lot of times you could actually put a 10 amp fuse at the furnace for extra protection due to the lack of amps used.
    Also, if you have too big a circuit, you might not blow the fuse/trip the breaker in an overload situation, like a frozen blower motor.
    Glenn Harrison, Residential Service Techician
    Althoff Industries, Crystal Lake, Illinois
    Althoff Industies Link