no heat
Chris_10
Chris_10 Member Posts: 14
Looked at a no heat situation yesterday. Had a gas fired burnham boiler, standing pilot with vent damper, three Honneywell zone valves. Was only able to get it to run by jumping the two front terminals (end switch?) on any of the three the zone valves.
Could the problem lie with the thermostats? Thanks
  • Tom Simensen
    Tom Simensen Member Posts: 74
    Did you have 24 volts at your transformer?
  • tim from Reed Wright
    tim from Reed Wright Member Posts: 113
    zone valve problem
    ? did you have all thermostats calling for heat or just one. If only one then it may be a bad zone valve. The other post also is very likely.
  • Steve Miller
    Steve Miller Member Posts: 115
    You have a bad end switch or the gears aren't activating the switch. It's best to replace the whole operator or best yet, go to zone pumping.
  • Chris_10
  • Chris_10
    no heat
    I Was getting power at the transformer and when the main power switch was turned on all the zone valves would open.It could be the switch in the zone head is not being activatived by the gears.
    Do they burn out? And wasn't noticed untill the last zone switch was gone and the whole house was being controlled by that last remaining zone. The ho did mention some complaints to this effect. Thanks!!
  • Steve Eayrs
    Steve Eayrs Member Posts: 421
    Did you let the factory installed smoke out of the transformer?
  • Chris_10
    no heat
    Zone heads were the cause.... All set.. Thanks!