no heat
Chris_10
Member Posts: 14
Looked at a no heat situation yesterday. Had a gas fired burnham boiler, standing pilot with vent damper, three Honneywell zone valves. Was only able to get it to run by jumping the two front terminals (end switch?) on any of the three the zone valves.
Could the problem lie with the thermostats? Thanks
Could the problem lie with the thermostats? Thanks
0
Comments
-
Did you have 24 volts at your transformer?0 -
zone valve problem
? did you have all thermostats calling for heat or just one. If only one then it may be a bad zone valve. The other post also is very likely.0 -
You have a bad end switch or the gears aren't activating the switch. It's best to replace the whole operator or best yet, go to zone pumping.0 -
0 -
no heat
I Was getting power at the transformer and when the main power switch was turned on all the zone valves would open.It could be the switch in the zone head is not being activatived by the gears.
Do they burn out? And wasn't noticed untill the last zone switch was gone and the whole house was being controlled by that last remaining zone. The ho did mention some complaints to this effect. Thanks!!0 -
Did you let the factory installed smoke out of the transformer?
0 -
no heat
Zone heads were the cause.... All set.. Thanks!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements