EDR rating
Can someone tell me the output of 2" iron pipe baseboard element? Have 4" x 4" steel fins, spaced at 15/in.0 -
this is the closest i can find
from ''hydronic rating handbook'' page 473...nothing listed that exactly matches your description that i have found,,,but it does list 2'' steel with 4.25'' fins at 24 per inch as 1100 btu per foot..hope this helps.0 -
With a calculator...
you could figure the EDR in square feet by yourself.
2 X Pi X R X length = surface area of the pipe.
L X W minus the hole = area of the fin.
Pi X the radius squared = the hole.
Don't forget to boil things down to common denominators. It's tough to add square feet to square inches...
ME
0 -
Another close one
but not quite the same. It may help you, though. Divide the steam output number by 240 to get EDR.
http://www.slantfin.com/comfin/elements.html
Noel0 -
Thanks for the info.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements