EDR rating
Unknown
Member
EDR rating
Can someone tell me the output of 2" iron pipe baseboard element? Have 4" x 4" steel fins, spaced at 15/in.0 -
this is the closest i can find
from ''hydronic rating handbook'' page 473...nothing listed that exactly matches your description that i have found,,,but it does list 2'' steel with 4.25'' fins at 24 per inch as 1100 btu per foot..hope this helps.0 -
With a calculator...
you could figure the EDR in square feet by yourself.
2 X Pi X R X length = surface area of the pipe.
L X W minus the hole = area of the fin.
Pi X the radius squared = the hole.
Don't forget to boil things down to common denominators. It's tough to add square feet to square inches...
ME
Another close one
but not quite the same. It may help you, though. Divide the steam output number by 240 to get EDR.
http://www.slantfin.com/comfin/elements.html
Noel0 -
Thanks for the info.0
- 120 Geothermal
- 394 Solar