Testing type B vent
leroy
Member Posts: 6
Where do you test for comb. eff. on cat.1 furnaces withdraft inducer fan and all type B vent.Even though this is negative pressure draft is it possible to have a 0 or even positive pressure draft reading if the reading is taken at a point right on discharge side of draft inducer fan.Can you drill hole in type B vent then seal back up with screw.Thanks.
Drilling B vent
We have letters on file from three B-vent manufacturers allowing the drilling of B-vent for the purpose of CO, draft and combustion testing. To seal the hole, they recommend high temp rtv.
If anyone needs a copy, email me and we'll get you a copy.0 -
You beat me
to him Rudy, but youve got the back up.
All b-vent flues must have a draft. I am sure there are folks here who remember the great sealed plastic flue pipe adventure and then the class action laws suits.
B-vents gotta draft.
Mark
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0