Testing type B vent
leroy
Member Posts: 6
Where do you test for comb. eff. on cat.1 furnaces withdraft inducer fan and all type B vent.Even though this is negative pressure draft is it possible to have a 0 or even positive pressure draft reading if the reading is taken at a point right on discharge side of draft inducer fan.Can you drill hole in type B vent then seal back up with screw.Thanks.
0
Comments
-
Drilling B vent
We have letters on file from three B-vent manufacturers allowing the drilling of B-vent for the purpose of CO, draft and combustion testing. To seal the hole, they recommend high temp rtv.
If anyone needs a copy, email me and we'll get you a copy.0 -
You beat me
to him Rudy, but youve got the back up.
All b-vent flues must have a draft. I am sure there are folks here who remember the great sealed plastic flue pipe adventure and then the class action laws suits.
B-vents gotta draft.
Mark
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements