Boiler Return Trap
check valves below the the boiler return trap. If the check valves leak water gets pushed out of the boiler. When the water level drops down the low water cut off will shut off the burner.
On real cold days if the check valves leak the boiler will not reach the proper operating pressure during the duty cycles. The boiler will cycle more fequantly and less steam will be produced.
jake
  • Wayne_14
    Wayne_14 Member Posts: 39
    Availabilty
    I have a Barnes and Jones Boiler return trap and I think it is ready to crap out. Are they availble. If not what has to be done to make the system work. (gravity)
  • Dana
    Dana Member Posts: 126
    www.barnesandjones.com
    Steamhead Member Posts: 18,211
    Consulting
  • Wayne_14
    It just does not appear to be working. All piping around it are hot and can not be held, yet the entire trap is cool to the touch. The system is working right now but every now and again has its moments and we can not get heat no matter what we do.
  • Wayne_14
    Thanks
    Many thanks, I believe the check valves are working. I know they were good a couple of months ago. I will recheck them.
    AT one point I had the boiler cycling on/off all day and night and no heat on any of the rads.