Before/After - DF
Michael B
Member Posts: 179
to my MAN on the east coast. I love what you guys do and you teach us all a little something everytime you post your work on the wall!!! Keep up the good work and don't be a stranger.
Michael Bleier
Able Distributors
www.abledistributors.com
"The Supplier Who Works With You"
Michael Bleier
Able Distributors
Before
Some of you may remember this job. I posted it back in January when I first looked at it. I was called in to troubleshoot this new installation. It was 17*F when I checked it out. The system could only maintain 51*F inside. I soon found out why. The only solution was to rip it out and start over. We were able to salvage a couple hundred feet of Multi-Cor and a few manifolds. Everything else was trashed. -DF
After
We spent the last 2-1/2 weeks rebuilding this system. We re-did the radiant using Quik-Trak plates. We added Runtal and Myson radiators to supplement the radiant. We replaced the boiler and added an indirect. The Danfoss panel controls the radiant zones. We gutted the Unico system and started over. The homeowners can't wait till next winter to give it a test drive. -DF
Why
clamp the tubing between the Quick trak?0 -
Clamps
The clamps between the plates keep the pipe from falling out of the plates. I once installed about 4500 sq. ft of RTI plates over the course of three bitter cold winter days. I returned to jobsite the following Monday to find close to 1/3 of the pipe had fallen out of the plates (even with silicone). Once bitten, twice shy. -DF
Looks great
Dan, but could we hope, after last winter, that they don't get a true test for a couple of years.0 -
The picture alone
is worth a million!
Fine work sir!
Mark H
Excellent work again , Dan
Its a shame that a fairly new system had to be totally redone . I bet the homeowner is very pleased they found your company , after the first fiasco . What happened to the Burnham boiler ?0 -
Nice!!
Good lookin' job Dan & Steve.,,,See you at WetstockIII
Paul
Another
Photo that I can show to my guys, so they know what good
work looks like.
Keep up the great work Dan.
Scott
Looks great Dan
I see you 've picked up on the viesman equipment. I'd heard troubling tales of the local distributor. Hope all went well with that. The Danfoss panels really clean up the clutter, don't they? I'm still looking for a chance to use them. See you soon. WW
From trash to treasure!
Give the boys a pat on the back from me. Just beautiful! What's this, another Viessmann virginity lost? ;-)
hb
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"There was an error rendering this rich post.
Boiler
Thank you for the nice comments, everyone. Ron, the Burnham boiler was only about 10 years old but was in rough shape. There was no return water temperature control and the sections were corroded from flue gas condensation. The homeowners were tired of the problems and wanted a reliable system. I felt the best solution was to replace rather than repair the boiler. -DF
Viessmann
Wayne,
I bought the Viessmann equipment from Jeff Riley @ Thos. Somerville Co. Jeff is one of a kind in the supply house business. The local rep, John Sargiannis, has been very helpful and responsive. What kind of problems have you heard of? See you Tuesday. -DF
a shout out
> virginity lost? ;-)
> hb
> _A
> HREF="http://www.heatinghelp.com/getListed.cfm?id=
> 103&Step=30"_To Learn More About This Contractor,
> Contractor"_/A_
Michael B0 -
Ditto
now the basement doesn't look like someone dumped a load of spaghetti in it. Beautiful work!
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Consulting0 -
Dan, just curious
what Danfoss panel did you use? 2 way, 3 way, 4 way, outdoor reset?
Michael Bleier
Able Distributors0 -
Rads
How are you controlling the radiators? TRV's? Just letting them run on reset? RTU's?0 -
Rads
Steve,
The panel radiators pictured are in an area of the house that does not have radiant floor heat. They are controlled by a setpoint control (air sensing thermostat). The water temperature is regulated by the Vitronic reset control.
Three other radiators provide supplementary heat to the radiant system. They are piped in parallel with the manifolds and regulated by TRV's. -DF
- 85.7K THE MAIN WALL
- 49 Biomass
- 73 Chimneys & Flues
- 92 Geothermal
- 150 Indoor-Air Quality
- 3.3K Oil Heating
- 59 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 39 Industry Classes
- 15 Recall Announcements