wiring a thermostat
Fred f
Member Posts: 1
A T8400B1018 Honeywell electronic power robbing thermostat requires a 1000ohm 3watt resistor be placed between the lower TT terminal and the lower FF terminal on a system with a R8184G primary control. I accept the instructions , I just want to know why and what the relationship is between those two terminals. Thanks in advance.
resistor
It is used to prevent the thermostat's display from blanking out whenever the primary operates.0 -
Hmmm...
Good question. Bill gave us the reason but what is the relationship ? Both are a power source .The TT is 24 V while the FF is 3.5V . I know if the Lower T makes contact with the upper F it will lock out..Good to know when looking for a safety reason.. I will assume(and I hate assuming) the resister will allow a trickel of juice for maintaining voltage for the thermostat's program???0 -
The reason is...
according to the internal wiring diagram I just looked at, the bottom "F" is common going back to the internal transformer, and the bottom "T" is the same as "W" coming from the t-stat to energize the primary relay. So it is essentially the same as coonecting the resistor between "W" and "C" on a scorched air system.
And if your curious, you can go to:
http://hbctechlit.honeywell.com/techlit/PDF/69-0000s/69-A0617.pdf
to see the wiring diagram I looked at.
Glenn Harrison, Residential Service Techician
Althoff Industries, Crystal Lake, Illinois
Althoff Industies Link0
- 87K THE MAIN WALL