wiring a thermostat
Fred f
Member Posts: 1
A T8400B1018 Honeywell electronic power robbing thermostat requires a 1000ohm 3watt resistor be placed between the lower TT terminal and the lower FF terminal on a system with a R8184G primary control. I accept the instructions , I just want to know why and what the relationship is between those two terminals. Thanks in advance.
0
Comments
-
resistor
It is used to prevent the thermostat's display from blanking out whenever the primary operates.0 -
Hmmm...
Good question. Bill gave us the reason but what is the relationship ? Both are a power source .The TT is 24 V while the FF is 3.5V . I know if the Lower T makes contact with the upper F it will lock out..Good to know when looking for a safety reason.. I will assume(and I hate assuming) the resister will allow a trickel of juice for maintaining voltage for the thermostat's program???0 -
The reason is...
according to the internal wiring diagram I just looked at, the bottom "F" is common going back to the internal transformer, and the bottom "T" is the same as "W" coming from the t-stat to energize the primary relay. So it is essentially the same as coonecting the resistor between "W" and "C" on a scorched air system.
And if your curious, you can go to:
http://hbctechlit.honeywell.com/techlit/PDF/69-0000s/69-A0617.pdf
to see the wiring diagram I looked at.
Glenn Harrison, Residential Service Techician
Althoff Industries, Crystal Lake, Illinois
Althoff Industies Link0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements