Radiant Pics
Daniel Paul_2
Member Posts: 20
The unit has a built in circ to move the water through the coil in the heat exchanger. This same circ can be used as the primary circ depending on the piping size and gpm for the primary piping. If the system is to big for that circulator than a circ would be added to the primary piping and the one inside the boiler would be used to inject into the primary loop. On a Baseboard system it can be as the main circ up to a certain footage(not sure what that # is off the top of my head).
Thanks for all the looks and comments
Danny (Keeping feet warm everywhere)
Radiant Pics
Just finished getting the system up and running before the big cold snap in the northeast.
It was a good test for the outdoor reset, good thing we designed for 0 outside.
This is a two bath and two bedroom addition. hope you like
Danny0 -
What
kind of boiler is that? Nice job!0 -
Laars Endurance
We sold a commercial job with several laars endurance. Good boiler. Please note that with that 58 helical coil heat exchanger, the water quality on the initial fill after cleaning is very important. Hotrod has posted several times on this subject and I have seen what happens 1st hand if you dont.
Great looking job.
PR0 -
The boileris a teledyne laars EBP 110 with a stainless steel plate exchanger for domestic hot water. It has a sealed combustion copper fin tube exchanger and when set up properly you can get close to 90% efficency.0 -
Looks nice! I'm the newbie here...what's the "valve" in the return line on the variable speed injection loop off? Is that a flow check valve?0 -
Circuit setter
This valve is to show resistance against the injection pump, so the pump better matches it's curve. It can also be used in the closed position as an isolation valve.
Danny0 -
Primary Circ
It looks great! Why is there no circulator on the primary loop?0
- 167 Indoor-Air Quality