Pex lines noisy
Guys:
Got a job with all Pex tube throughout a very large home. The complaint is noise from expansion/contraction.
Will expansion joints at the boilers help with this?
The tubing is under floors, up inside walls, etc.
Never had this complaint before. Any ideas???
John
  • Jamie Pompetti
    Jamie Pompetti Member Posts: 82
    Would you please tell us a little more about the system? Maybe some pictures.
    Is it injection or mixing valves? what size pumps?
    Jamie
  • ScottMP
    ScottMP Member Posts: 5,882
    Noise
    Do you have any re-set on the system ? The large temperature swings really make this a problem. Constant circ. Helps eliminate this also.
    Years ago I had a problem with this and added expansion loops to the pex before the risers in the basemant, it helped take up Some of the expansion.
    Pex-al-pex is the way to go.
    Scott
  • Brian
    Brian Member Posts: 285
    Pex noise
    Years ago I had that problem on a clip-up system.Ended up being the clips I was using.Check to make sure they're compatible.Also check if the lines are bundled together to tight.
    Good Luck
    Brian
  • "very large home" makes me think perhaps your loops are a lot longer than normal perhaps? That would explain why you might see it here and not on other jobs. For long runs in dry installations I usually try to break them up into two separate loops. A bit more work on the install but more expansion is taken up by more loops! 1.1"/100feet/10deg delta T adds up fast when you have 50 foot straight shots down a long joist bay.
    As someone else noted, reset control can help this a lot if you don't already have it.
  • expansion noise
    i have that noise in my house from the 2 bays that have extruded aluminum plates. i don't have outdoor reset
  • expansion noise
    i have that noise in my house from the 2 bays that have extruded aluminum plates. i don't have outdoor reset. bob
  • John G. Merritt
    John G. Merritt Member Posts: 140
    Pex noise
    Guys:
    This is a Pex system, using Mixing valves, and fairly tight bundles of 1" supply, runs are about 40 to 50 feet before they go up into the walls of this monster 2 million dollar house. Has a snow melt also, all (6) patios.
    Don't know the Circulator sizes at this time.
    Have not spent enough time to check everything out yet.
    I just wondered if Expansion joints would help stop the noise. (Has outdoor reset also) Customer installed most of the tubing himself. (Nightmare) John
  • Bill Clinton_2
    Bill Clinton_2 Member Posts: 19
    pex noise
    I discovered the hard way that barrier pex tubes when rubbing against each other can make a good deal of noise. If your tube is barrier style, this could have a lot to do with the problem.
    Bill