fuel oil nozzle
Patrick_9
Member Posts: 2
In my research I have found where changing from a hollow nozzel to a semi solid increased efficency by 5-9%. I have decided to get away from the hollow nozzel and go to semi solid.
So you are saying to go with manufacturers recomended nozzel even though I have finally increased my draft??
fuel oil nozzle
Good morning!! I have a question regarding fuel nozzles, if the burner calls for a .75 gph/60 degree nozzle is there a problem putting in a 80 degree?? Thanks in advance for all your help.0 -
I suggest
that you put in the exact nozzle specified by the manufacturer. Make sure you use the manufacturers they specify and the letter designatrion, such as "1.10 80°ES". They have tested fort a wide variety of conditions and there specification will give yo the best performance.0 -
nozzle
it depends on the chamber its firing into tech should have checked the boiler specs to see what the correct nozzle is for the boiler
More about Nozzles.....
With today's flame retention burners and smaller combustion chambers it's so crucial to understand the effects, that increasing fuel pump pressure can have on a system. Possibly incomplete combustion that will lead to the production of CO (carbon monoxide)
Something you should know is the tolerances nozzles fall within.
For example if you had a system with a maximum firing rate of 1.20 GPH and you decide it would be better to install a 1.00 GPH you know if you increase the pump pressure to 145 PSI you'll be back to 1.20 GPH with a smaller nozzle or will you?
Nozzles from 1.00 GPH to 1.50 GPH can have a tolerance of +5% and - 2%
So if the 1.00 GPH nozzle you installed was +5% at 145 PSI your actual firing rate would be 1.26 GPH. Again this could lead to a system cycling on hi limit and/or worse yet the incomplete combustion that will lead to the production of CO (carbon monoxide) Now with a better understanding if you were to have increased the Pump PSI to only 120 PSI you'll find this would only bring the 1.00 GPH Nozzle to 1.10 GPH and even it were over by 5% that would still only be approx. 1.155 GPH, still well under the Maximum Firing Rate.
Here is something else to think about. Did you know when you increase your pump pressure although the spray pattern gets shorter, the angel will become wider?
This means your 80° Nozzle may have just become an 84° Nozzle. You may have done this because the flame was impinging o the back wall of the chamber unfortunately now it may be impinging on two sides of the chamber. In this case you may have wanted to change the nozzle to a 70°
These are the reasons why it's so important to understand this and to always after any adjustments are made to the burner perform a combustion analysis
Your friend in the industry,
Alan R. Mercurio
Oil Tech Talk0 -
Alan has explained in detail
why you should follow the manufacturers specifications exactly, especially in todays boilers.0 -
Yes and No
Patrick, I'm not sure if your question is directed at me or steve? So just to cover myself and not ignore you here's my thoughts on my post above.
I am just sharing some knowledge as to why it's so important to understand the effects of changes we make in the field. and to always remember that after any adjustments are made to the burner we should perform a combustion analysis. I understand lab conditions don't always exsist, after all I'm from the trenches of reality
Alan R. Mercurio
Oil Tech Talk0 -
Patrick
I am not trying to get into a debate. If it works for you, great!
Manufacurers must be sure their product will operate best under the wide variety of field conditions the equipment is exposed to. This applies to many variable and they do change form day to day on each individual job.
Remember, the manufacutrers do not sell fuel oil!
Steve0 -
Thanks for the info!!!0
