Can air be sucked into a boiler
that air can be sucked into a boiler through the float vent - even when theres pressure on the boiler . He said that if the circs come on suddenly , and theyre piped after the float vent , air can be drawn in - even if the pressure is relatively high . I tested the boiler we worked on today - turned 3 zones on at once - the pressure stayed an even 20 psi , and I didnt hear anything from the air can .
The same guy suggested we start using an 1 1/2 by 1 1/4 double tap bushing on the header - to drop a nipple into the boiler a little , so we can trap and eliminate the air through the separate 3/4 tapping right next to it on the Burnham V8s . I think thats a good idea , but does anyone make something a little more heavy duty ? Like a threaded nipple that might extend into the boiler itself ? Those bushings are so thin , they crack real easy . I already asked about the Taco Vortec or the Spirovent , and they aint gonna go for em . Thanks in advance .
AIR
AT MY COMPANY WE INSTALL A VENT IN THE BUILT IN SCOOP OF THE BOILER BUT WE ALSO USE AIR SCOOPS ON THE HEADER OF THE BOILER. JG0 -
The only way
that can happen is if the circulator is developing a differential pressure greater than the system's static fill pressure, and it's pumping at the compression tank. Other than that, it can't happen.Retired and loving it.0 -
Like Dan said ....
Pumping away is the solution !
Point of no pressure change is the key. Took me a while to grasp the concept, but the light shined when it was explained properly .0