My DHW circulator (007) is mounted horizontally (meaning flow is horizontal).
The horizontal piping run it is mounted on is essentially the highest point in the loop.
It is pumping away, and is downstream of a Taco Air Scoop.
I had to drain the loop to repair a leak. I purged as much air as possible at the top of the check valve (on the return, see picture Boiler4.JPG).
The circulator is still making "I have air in me" noises.
Actually, it was a little noisy (compared to the one mounted vertically) even before the repair.
Will the Air Scoop eventually purge the air from this line, or is this circulator orientation just asking for trouble?
air noise
did you loose the screw on top of the flow check valve when you purged the system? also i believe the 007 feeding the tank is in upside down you also might think about installing a spirovent air elimanator in place of the air scoop
From the look of your pic, It seems that the air in that loop
going to the W/H is trapped at the pump. It will eventually absorb into the system and the air eliminator will get rid of it. This may take a while. I'd place a 3/4 x 1/8 x 3/4 air vent tee and a coin air valve to vent that pump. Just on the supply side of the tank repalce that ell. Pics sometime show things that are not there. It looks that the pump is the heighest point along that line, and with the reduction in size of pipe that traps a lot of air. anyway bigugh0 -
Yes
That is correct. I purged as much air as possible at the top of the check valve. I have repeated this several times to see if any more would 'shake loose', but nothing.
Is my 007 really upside-down? Perhaps that is part of the problem. I could not find any install instructions regarding orientation at the Taco site, or anywhere else.0 -
Highest point
Yes. You are seeing things correctly. The pump is essentially at the highest point in the line (other than the air scoop). The pipe reduces to 3/4 copper on the outlet side.
Thanks for the vent idea. The check valve vent just does not seem to be doing the job. I suppose air would have to go down through the indirect coil to even get to the check valve (which is on the return), and why would it want to..0 -
Upside down?
Can anyone verify whether this circ is indeed installed upside-down? Still can't find any Taco install instructions...0 -
By upside down
I think Ed is refering to the electrical junction box on the pump. I think the prefered location is on the side or top. Remove the four screws and turn the motor. With the water off and pressure drained, of course!
There should be an arrow on the pump volute indicating flow direction also, make sure she's pushing the right direction. If not remove the four flange bolts and flip the whole pump.
hot rod
Corey
#1 What they are saying about the pump is that IF a leak occured it would leak into the electrical box and cause problems. This does not effect the operation of the pump, its just good practice
#2 After purging the air form the indirect loop the air left should be small bubbles that a standard air elimination device ie: air scoop should get rid of. Again good prectice but a vent at the top of the line is not necessary
#3 For proper air elimination from your system and for the air scoop to do its job it should be located 18" from the ell at the top of the riser coming out of the boiler. Yours looks like a 4" nipple. The water coming up that riser from
the boiler riser is spinning around and needs that 18" to have time to rise to the top of the supply pipe and be eliminated by the vent at the top of the air scoop.
#4 For a proper "pumping away" set-up, your make up water connection should be located between the air scoop and the bladder tank ( the point of no preasure change in the system ). You cant do half of it and expect the same results.
#5 If your circulator is making noise and the systems is making domestic hot water, I would look at the volute of
the circulator and see if any solder is stuck there. Enough air to make noise would not allow circulation( I think ).
If you relocate the electrical box check the volute and be sure its clean.
Theres my opinions for what its worth
Good Luck
Scott
Thanks so much, Scott
You da man.
The manufacturer's instructions (HTP- it's a Munchkin 140, which you cannot see in the photos) specify that the fresh water connection should be placed right at the boiler supply. This is not ideal for so many reasons, and I wonder why they would say to do it this way.
Maybe this will
Maybe this will
help you out a bit.0 -
Maybe this will
help you out a bit.