tee placment
DKH
Member Posts: 15
I have piped many primary/secondary commercial systems and placement of the supply/return tees I thought I understood but working on a residential boiler the supply/return tee placement of a single zone is the same, but is there,an issue due to lack of space that the next zone supply can be as close to the previous zone return.ie. tee/supply/nipple/tee/return/nipple/tee/ supply/nipple/tee/return/nipple etc.(nipples 6" or less due to space restictins)(zone placement on header based on water temperature requirments/w.h. first ,radiant last - 6 zones total) thank you
no concern with placement between secondaries
but why not use a single, secondary supply and and return manifold set? Might give you more room and the temperatures are easier to predict.Retired and loving it.0 -
dan
As in a one pipe direct return piping arrangement./thank you0 -
Actually
two-pipe direct return, but I think we're talking about the same thing.Retired and loving it.0 -
understand / thanks0 -
dan /advise control strategy/please comment
My control strategy is any secondary circulator runs boiler and primary circulator are energized /secondary zone shuts down primary shuts down please comment/cold start boiler/high limit control/boiler shock prevention?0 -
that's
the way I'd do it.Retired and loving it.0