tee placment
DKH
DKH Member Posts: 15
I have piped many primary/secondary commercial systems and placement of the supply/return tees I thought I understood but working on a residential boiler the supply/return tee placement of a single zone is the same, but is there,an issue due to lack of space that the next zone supply can be as close to the previous zone return.ie. tee/supply/nipple/tee/return/nipple/tee/ supply/nipple/tee/return/nipple etc.(nipples 6" or less due to space restictins)(zone placement on header based on water temperature requirments/w.h. first ,radiant last - 6 zones total) thank you
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,687
    no concern with placement between secondaries
    but why not use a single, secondary supply and and return manifold set? Might give you more room and the temperatures are easier to predict.
    Retired and loving it.
  • DKH
    dan
    As in a one pipe direct return piping arrangement./thank you
  • DanHolohan
    Actually
    two-pipe direct return, but I think we're talking about the same thing.
  • DKH
    understand / thanks
  • DKH
    dan /advise control strategy/please comment
    My control strategy is any secondary circulator runs boiler and primary circulator are energized /secondary zone shuts down primary shuts down please comment/cold start boiler/high limit control/boiler shock prevention?
  • DanHolohan
    that's
    the way I'd do it.