Primary secondary with a WM GV boiler
Andy Morgan
Member Posts: 2
Where is the right place to put the expansion tank to acheive "pumping away" when you pipe this boiler prim/sec? The instructions are not clear about this. System will be 6 zones of radiant, two hydros, and an indirect.
Thanks
Andy Morgan
Thanks
Andy Morgan
The easiest way...
is to make a long header with supply say on the right and the returns all on the left, pipe the supply and return from the boiler into two tee's close to gether in the center. Then on the supply side before the tee,s for the supplies just put your air scoop, with the water feed and the expansion tank under it. Then place all your circ. pumps for the various zones on the supply for each zone.
Don't forget flo-checks or you'll have big problems!!!
Hope this helps!!
John Siegenthaler
Put together a wonderful book for Weil showing many different primary/secondary set-ups (including this one). Ask your local wholesaler for a copy...if he/she does not have it you can contact me mikeb@abledistributors.com and I will be happy to fax it to you.
The Weil McClain book is great!
I didn't know John S wrote it for them. Some of the best illustrations I've ever seen. If it's what I think it is It's "AlumiPex Radiant Tubing Controls, Pumps, Wiring design guide" Part no. 650-000-240/1098 I don't know if there's a newer edition but the answer to your question is on pgs 62 and 63 showing an injection panel. page 82 adds a bit. I would recommend this book to anyone working in RFH. I asked Dan to sell it on his website but I guess there's some reason not to.0