Dunkirk Boiler Cycling On and Off

Options

I have a Dunkirk PWB-6D Model #: BW2AAN000175ABAA hydronic boiler.

Recently the burner stopped firing though the pump continued to circulate water while there was a constant call for heat as the thermostat temperature dropped.

Here's what I've done so far:

  1. I cleaned all the burners and holes. I also tried to clean some corrosion off the pilot light and ignition with a scotchbrite sponge. There is a clean blue flame coming out of each burner now.
  2. I confirmed 24VAC across B1 and B2 on the aquastat.
  3. I obtained continuity on the rolloff switch.
  4. I did not obtain continuity on the damper spill switch and temporarily bypassed it by connecting the leads together to try and get the boiler to fire up.
  5. The boiler would then fire up for about 5 minutes then cycle off. It would then fire up again after 5-10 minutes, run for 4-5 minutes and cycle off again. Firing up sometimes was immediate within 3 seconds, but other times it took 15+ seconds to fire the burners after the pilot ignited.
  6. I checked the pressure and it's about 15-18psi when running. I had it higher but backed it down a bit thinking the aquastat was cycling the boiler off when the pressure increased.
  7. The water temperature only reaches about 95F max.

I'm not sure if it could be the control board, the aquastat, the gas valve or a pilot burner that could be on its way toward failure? The boiler is now 32 years old, but I can't afford to replace it yet. It doesn't leak and has been heating the house adequately every year.

Thank you for any insight or suggestions on how to figure out what the problem is.

1000018158.jpg 1000018157.jpg

1000018154.jpg 1000018156.jpg

Comments

  • Dave Carpentier
    Dave Carpentier Posts: 713

    Im not a tech, but would be curious if you can verify that the damper is fully opening ?

    30+ yrs in telecom outside plant.
    Currently in building maintenance.
  • bburd
    bburd Posts: 1,351

    Something is shutting down the burner well before the aquastat reaches the high limit setting. If you have a multimeter and know how to use it, you may be able to troubleshoot this yourself.

    —
    Bburd
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,444

    If you have 24v on B1 & B2 on the aquastat it should fire up. If it doesn't check the flame roll out switch and the blocked flue switch. Both of those have to be closed. If you put a meter across the terminals on either one of those controls it should read 0 volts if closed and 24v if open.

    Since the circ is running the thermostat is calling. If you don't have power to B1 & B2 the damper end switch could be the issue or the B-R terminals on the aquastat High Limit switch. B-R on the aquastat should be 0 volts if calling.

  • HVACNUT
    HVACNUT Posts: 7,859

    If you jumped the Spill Switch and it started, then the chimney and draft needs to be checked. Its also possible excessive heat from the boiler trips it after the damper closes. The spill switch should have a reset button between the wire terminals. There should also be a manual/auto switch on the vent damper. While the boiler is running, switch it to manual open. If the problem goes away, it's just residual heat dumping out the draft hood.