Dunkirk Boiler Cycling On and Off
I have a Dunkirk PWB-6D Model #: BW2AAN000175ABAA hydronic boiler.
Recently the burner stopped firing though the pump continued to circulate water while there was a constant call for heat as the thermostat temperature dropped.
Here's what I've done so far:
- I cleaned all the burners and holes. I also tried to clean some corrosion off the pilot light and ignition with a scotchbrite sponge. There is a clean blue flame coming out of each burner now.
- I confirmed 24VAC across B1 and B2 on the aquastat.
- I obtained continuity on the rolloff switch.
- I did not obtain continuity on the damper spill switch and temporarily bypassed it by connecting the leads together to try and get the boiler to fire up.
- The boiler would then fire up for about 5 minutes then cycle off. It would then fire up again after 5-10 minutes, run for 4-5 minutes and cycle off again. Firing up sometimes was immediate within 3 seconds, but other times it took 15+ seconds to fire the burners after the pilot ignited.
- I checked the pressure and it's about 15-18psi when running. I had it higher but backed it down a bit thinking the aquastat was cycling the boiler off when the pressure increased.
- The water temperature only reaches about 95F max.
I'm not sure if it could be the control board, the aquastat, the gas valve or a pilot burner that could be on its way toward failure? The boiler is now 32 years old, but I can't afford to replace it yet. It doesn't leak and has been heating the house adequately every year.
Thank you for any insight or suggestions on how to figure out what the problem is.
Im not a tech, but would be curious if you can verify that the damper is fully opening ?
Currently in building maintenance.0 -
Something is shutting down the burner well before the aquastat reaches the high limit setting. If you have a multimeter and know how to use it, you may be able to troubleshoot this yourself.
Bburd0
- 136 Chimneys & Flues