swapping baseboard registers back to the taller registers
Replacing Bathroom Hydronic Baseboard With a Small Upright Cast-Iron Radiator
My house was built in 1924 and has a hot-water boiler with one thermostat controlling the entire house. I currently have a combination of traditional upright cast-iron radiators and hydronic baseboard heating.
I'm remodeling my downstairs bathroom and would like to remove the existing baseboard heating to allow me to relocate my vanity and expand my linen storage.
The bathroom has two sections of baseboard heating that run continuously around a corner. There is a bleeder valve at one end and what appears to be a shutoff valve at the opposite end.
I have an unfinished basement with accessible heating pipes, which I believe are a combination of older iron and newer copper piping. There are also two long sections of older basement piping with suspected asbestos insulation that I would prefer not to disturb.
My questions are:
- Since my existing heating system already accommodates both types of radiators, would replacing the bathroom baseboards with one upright cast-iron radiator be a relatively straightforward job?
- Could the existing bathroom heating connections be reused without substantially modifying the rest of the heating system?
- Would this typically be a relatively inexpensive plumbing job or a more extensive heating system modification?
- How do I determine the appropriate size and BTU output of the replacement radiator?
- Can I calculate the required radiator size based on the existing length of baseboard heating, or would I need a heat-loss calculation for the bathroom?
- What measurements or information would I need to provide to determine the correct radiator size?
- Are there any concerns with purchasing a used or refurbished cast-iron radiator for this application?
It's not a particularly large bathroom, so I would prefer a taller, narrower radiator that takes up minimal wall and floor space while still providing adequate heat.
I'm not looking to convert the entire house, just this one bathroom. I'm trying to determine the feasibility, complexity and potential expense before finalizing my remodeling plans.
Any professional advice would be greatly appreciated.
Comments
-
- Yes
- Probably, but that depends on how the rest of the system is plumbed
- As 2.
- Lots of ways to do this, but
- Yes. And this is the easiest approach, if the existing installation heats the room properly
- Dimensions of the space, exterior wall lengths, insulation, roof or attic, crawlspace… windows type and size… etc. But see 5.
- None at all. Just make sure it doesn't leak.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If the baseboard that is installed now heats the bathroom ok then measure the length of the existing baseboard. Only measure the "finned length" Multiply the finned length x 550 will give you the baseboard output in btus. Example : 5' finned length x 550=2750 btus/hour.
Then you would find a radiator rated for an EDR of 12 = (2750/240)
With basement access this is a simple job.
0 -
Since this was designed as a gravity hot water system, the BTU conversion from EDR is 170 I believe, not 240 as used for 215°F steam.
—
Bburd0 -
the measure the finned section of the baseboard then find an equivalent radiator will likely be close enough.
the better way would be to calculate the room by room heat loss of each room and compare to the emitters that are currently in those rooms. if they are oversized by a certain amount you should oversize for this room by that same amount to keep it balanced.
since you have an open basement getting it wrong and having to change it probably wouldn't be that bad. err on the side of too big, you can always throttle it with the valve. it would be harder to add capacity.
fin tube and cast iron on the same thermostat are never a great idea because the cast iron heats and cools slowly and the fin tub heats and cools quickly so the temp swings are much larger in the rooms with the fin tube. if it works for you leave it, but if you're uncomfortable, now you know why.
0 -
One thing to add on sizing from the baseboard, if the bathroom heats fine now. Measure only the finned element inside the covers, not the covers. A common residential element like Slant/Fin Fine/Line 30 is rated about 580 BTU per foot at 180 average water, and cast iron on hot water is about 170 BTU per square foot of EDR at that same 180. So each foot of element is roughly 3.4 square feet of EDR.
Then you need a radiator whose sections add up to that. EDR per section depends on the height and the number of tubes, and the old cast iron ratings tables list it, so a tall narrow one just means more height per section and fewer sections.
0 -
Your right. My mistake.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 136 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements