connecting plain end pipes in riser - Roust-a-bout Alternative

Options

I have a larger steam boiler that has two 2-1/2" risers that connect to the header. Residential steam heat, less than 1 PSI operating pressure.

It uses these Roust-a-bout plain end pipe connectors to connect the vertical risers to the header. They have no physical load on them, the header is very well strapped to the ceiling, they are just keeping in the steam.

I don't think these connectors are supposed to be used for steam, especially not straight off of the boiler. They have been in service like this for years, and I don't trust them to not start leaking (I think they may actually already have a small leak, but with the steam straight off the boiler it is hard to tell).

Does anyone have a suggestion for a replacement for plain end pipe or for at least for a replacement gasket for inside of this coupling, I can't find much about them or as source for parts.

Yes, I know, I could install threaded pipe and unions, but these pipes are already in place and it would generally be a PIA to try and lift the huge header assembly up to install unions and risk breaking something in the process.

Thanks in advance for any help/suggestions.

20261124_165337.jpg

Comments

  • ScottSecor
    ScottSecor Posts: 1,101
    edited November 24

    We call them "Vitaulic" fittings. It is actually grooved pipe. A machine cuts a roughly one quarter inch wide groove on the pipe. The two gaskets (one for each piece of pipe) are cinched down with those two large diameter nuts and bolts. I would never use them on a steam pipe, but I have seen it done.

    This type is rated at 250 degrees and 1000psi according to the specs on Supplyhouse.

    https://www.supplyhouse.com/Gruvlok-390003028-2-1-2-7001-Grooved-Coupling-w-EPDM-Gasket

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,427

    @ScottSecor & @jacksonpollack

    Those are plain end couplings , No groove in the pipe.

    I have used them on hot or chilled water when forced to.

    Not steam rated. ACTUALLY i WAS WRONG. LOOK AT THE SPEC SHEET THEY DO HAVE A STEAM RATED GASKET

    @jacksonpollack just find a supply house. A typical supply house (plumbing) may not have them but can probably order them. You might find them on line. A pipe valve and fitting distributator would have them search for someone that sells Victaulic..

    just like it says you need gaskets for a 2 1/2" VIC roustabout #99. I have never bought gaskets for those seperately. I have for the grooved pipe couplings.

    The only thing other than threading is a MEGA PRESS Viega coupling which is rated for low pressure steam.

    We did have a temporary steam like at the University of MA (don't remember the pressure) and we used these for a temp line but it was run outdoors. They lasted a while

  • ScottSecor
    ScottSecor Posts: 1,101

    I stand corrected. Do not think I have seen these before.

    What type were the ones on the return yolk of the HB Smith 28 boilers (would have been 1980's or 1990's)?

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,427
    edited 12:08AM

    @ScottSecor

    I don't remember those on the Smith 28s for some reason.

    I remember the Hydrotherm modular boilers with the premade headers (hot water) that use some type of coupling with a rubber gasket it was kind of a light duty thing. Those boilers were popular in the 80s & 90s. I was never crazy about the roustabouts we only use a few sparingly when we had to. I was always worried about them pulling apart. But they are pretty heavy duty and I don't remember having any problems with them.

    I never knew they could be used on steam and was surprised to see that when I looked at the cut sheet

  • Mad Dog_2
    Mad Dog_2 Posts: 8,770
    edited 12:30AM

    "Roustabouts" are made by Victaulic and they have teeth that bite down in to the outside diameter of the pipe wall. Used many over the years on Hot water, steam under varying pressures with no issues. Can you step back and get a floor to ceiling shot of the boiler and piping? Mad Dog

  • jumper
    jumper Posts: 2,633

    Thermal expansion cycling between 200° and 70°? Don't like it. Those teeth need to grip.

  • jacksonpollack
    jacksonpollack Posts: 18
    edited 3:03AM

    Thanks everyone for the comments.

    The pipes in the joints are touching. When the boiler was last replaced the riser stubs from the boiler were cut so the boiler could be just slid under the risers that are attached to the header. If I had a good gasket that did not mind the heat, I would guess that just a cheap hose clamps on either side of the gasket would work for a while considering the pressures involved.

    When I last had them apart the gaskets were not in great shape, but I could not easily find a replacement without buying a whole new fitting.

    Perhaps I am missing it, but I have looked in Victornox catalogs and I am not seeing a part number for the just the gasket. By my reading I think I want the EPDM gasket for steam.

    Are the groove coupling gaskets the same size? Compatibility between different manufactures?

    If anyone has a part number or suggest online source that I could order two new gaskets I would greatly appreciate a suggestion.

    Thanks again.

  • 109A_5
    109A_5 Posts: 4,841
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • pedmec
    pedmec Posts: 1,496

    Looking at the spec sheet it clearly states not compatible with steam. Am i missing something?

  • Mad Dog_2
    Mad Dog_2 Posts: 8,770

    They are not a substitute for the proper Joints and materials. If you put up a photo that depicts the whole situation, a better solution can be discussed. Mad Dog

  • Dresser couplings are plain end pipe couplings that are steam rated but they do cost a pretty penny, especially as the size goes up.