Hi folks, lady homeowner here trying to troubleshoot my flooding boiler….
The last two heating seasons at the coldest outside temperatures the boiler kept flooding. I'd get to the basement and find the condensate tank pump was running nonstop and water was coming out of the safety relief valve on the boiler. After this happened several times we’d shut it down and take apart the float LWCO find that it wasn’t really dirty….nothing that really looked like it would affect the movement of the float.  We’d rinse it out and add a new gasket and reassemble and it would work the rest of the season with no more problems. Same scenario for both seasons.  Just starting this season with everything rinsed and cleaned and now I keep finding the boiler has shut off and is flooded, but not to the point of overflowing out of the boiler and not tripping the condensate tank to continuously run. I suspect that my float LWCO is the problem…maybe the switch? Though it's just been cleaned and the float seems to be moving freely. I see people mention that these LWCO's should be replaced every 10 years… is that true? Mine is now 12 years old. My question to you experts. With the issues I am presenting does it sound like my float LWCO is the culprit or should I be looking somewhere else? …. If it is the culprit… can I just replace the head unit or do I need to replace the whole thing. I have had a boiler tech tell me that if I intended to replace it, I need to do the whole thing. Thanks very much for any advice.
The system:
• Weil-McLain EGH-95 installed in 2014
• Pressuretrol cut in: .05 Diff: 2
• McDonnel Miller 150S LWCO
  with a secondary McDonnell Miller probe PSE-802-M-24 LWCO both installed in 2014
• Sterlco 41215-G condensate return tank and pump.
• This is a two-pipe steam system with 6 zones.
• Check valve between tank and boiler replaced three years ago.
• Boiler has been rinsed and float LWCO has been disassembled and cleaned after every season since install…This includes draining and rinsing the condensate return tank, cleaning fresh water solenoid valve as well. F&T’s have been cleaned and gaskets replaced just this season. LWCO is blown down weekly throughout the season.
Screenshot 2026-11-21 at 6.39.18 PM.png Screenshot 2026-11-21 at 4.27.57 PM.png
    EBEBRATT-Ed Posts: 21,407
    I have had problems with the 150s. But I would like to know how yours is wired. You have a condensate tank which just usually runs the pump off of the tank mounted float control.
    But you have a 150s MM mounted on the boiler which is a pump control.
    I am going to guess that the float switch on the tank rund the CW make up solenoid valve and the 150s runs the pump. is that correct????
    If that is the case and only the 150s runs the pump then you would have to buy a new 150s head. make sure the body is cleaned out. The older 150s use mercury switches and the replacement will be snap switches. They do cost $$$$ though. MM parts are expensive. The snap switches are usually more reliable.
    Jamie Hall Posts: 28,035
    THE important question is what control actually runs the condensate pump? If it's the M&M, technically you have a boiler feed pump, and the place to look is at the M&M, which made need replacement. On the other hand, if it is a float in the condensate tank, you technically have a condensate feed pump, and the place to look is the float or level control in the tank.
    Which do you have?
  • Steve214
    Steve214 Posts: 26
    What is controlling the water feed solenoid on the feed pump? There’s usually a float valve in the tank feed line.