New system
I’m installing a new heating system in my renovated 1870 farmhouse with a Rinnai Ip90s boiler. The system design is for both radiant floor & 2 cast iron radiators. I have rough drawing of what I think will work for me. Also the plan is to do this project in stages. First will be the radiators then the radiant with ball valves on the radiant side. Any suggestions on my design would be helpful Thanks tzix56
Comments
-
Cast iron radiators require med to high temperature water; a radiant floor requires low temperature water.
You will need a system that can provide two separate water temperature zones.
What type of radiant floor are you proposing?
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
This option shows a "horseshoe primary loop. The boiler "injects into it.
The mix valve could be a 3 way thermostatic. Of if the radiant is one zone only, a manual 3 way would be adjusted to the required radiant SWT. It would track with the boilers ODR function. Called proportional reset.
So both the radiators and radiant track with ODR. Siple and efficient.
Use a combo air/ dirt/ magnetic separator.
If the system will be zoned an ECM circulator will adjust to changing loads..
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I’ll be using thermostatic mixing valve for the radiant floor heat, that will be 3 zones on a Pex manifold with zone valves.
tzix560 -
Look for a thermostatic mix valve with a 3 Cv if you have multiple zones coming off it. Most, but not all 3/4 and 1" thermostatic are 3 Cv.
The ASSE 1070 valves tend to be lower Cv, these are intended for point of use, lower flow applications.
You want an ASSE 1017 valve.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I’m using the Primary-Secondary Heating Kit for I-Series Boilers (Heat-Only Models), 807000213 it has 1 1/4 header do you see any issues reducing to 1 inch for secondary?tzix56
0 -
Really no need to for the kit in the drawing I showed. Then the boiler could be mounted anywhere in relation to the horsehoe loop. The "header" is where you tee the 1" from the boiler into that loop.
The loop may be 1" depending on how many btu or gpm you are wanting to move around.
What size is the boiler? The piping would match its output.
80,000 or less could be all 1" piping.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I already have the kit and it’s a rinnia ip90s rated at 90k btu. The space that is to be heated is about 70k btu that will have 4 total zones 3 radiant floor and one cast iron. The reason for this project is to have better control over the temperature in the different areas of the house. Programable thermostats will be installed on all 4 zones so I don’t see all four zones on at same time but should be sized if it ever dose
Tzix56
0 -
you have the concept. Try and avoid "bull head" connections like this, the flow doesn't always split the way you want.
I think that Rinnai header needs to be just below the boiler? If not it could be vertically mounted to save soe ells maybe?
Use the circulators with internal checks or a check just downstream. No additional checks needed in the piping.
Basically extend the LLH in 1-1/4 to make the zone connections hi temp and mixed low temp. Still consider a multi function air. dirt purger
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 136 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements