Ad hock radiator

Options

It's a small bathroom, about 6X10, 8' ceiling. I gutted it and remodeled it and the steam radiator, one-pipe, (20WX28HX5Thick, 10 tubes) doesn't fit anywhere anymore. I've been looking for a slender, dinky radiator to fit behind the clawfoot tub and the outside wall but no luck. So, here's what I'm thinking ……. make one.

I'm a copper guy and have a 3' long piece of 2.5" K copper in my bag of tricks. The plan hatching in my head is to adapt one end of it to attach to the original 1" radiator valve by capping it and silver brazing a 2.5" cap fitted with a 1" FIPA at the bottom and then fit the other end with an 1.25" riser. Several inches up, tap into the riser with a fitting for a steam vent. Drill the 2.5" copper on 3" centers facing up and silver braze multiple 3/4" copper risers to act as the "sections". These "sections would all terminate into a top manifold which is also connected to the 1.25" riser described earlier. OK, guys, let me have it! I'll try to be brave and take it!

Answers to questions you have not yet asked:

  1. It'll be behind the tub and lower than the tub rim so no-one will accidentally come in contact with it. Heat generated will not only wipe the window above but will also radiate toward the cast iron tub, a very positive thing.
  2. I THINK the condensate will perform normally, but, obviously, the copper is going to heat up really fast and may create condensate issues.

I just can't wait to hear what you guys have to say. Don't ghost me just because you think I'm lame.

ccstelmo

Comments

  • mattmia2
    mattmia2 Posts: 18,486

    it would be better to use black iron pipe both for the lower conductivity and the lower coefficient of thermal expansion. there used to be fittings made to do that, you can still get left-right nipples and couplers. black iron would make less noise, balance better with the system, and make condensate over a longer period of time at startup so it would be less likely to have issues with hammer. you need to be careful that the condensate can get back to the supply end because the passages in pipe are much smaller than in a cast iron radiator. there are also numerous ways to bring the condensate back from the far end in a separate return pipe either below the radiator in the supply or to a wet return.

  • bburd
    bburd Posts: 1,345

    Standard practice in New York City for many years was to run a 2 inch black steel steam riser in the corner of apartment bathrooms, usually through multiple floors, tapped for a radiator air vent at the top. It cost less and needed less space than a radiator, and worked well.

    —
    Bburd
  • Jamie Hall
    Jamie Hall Posts: 28,032

    Your pipe idea will work fine — just hae enough pitch on the elements. I rather agree that black pipe would be better, though, as it gives more even heat.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • kcopp
    kcopp Posts: 4,744