Propane supply and boiler lockout

Options

I live in a remote ranch in Colorado and had a second buried 1,000 gallon propane tank installed last summer. The tanks are buried next to each other and manifolded together. When just the old tank is open everything works fine but when I open the valve for the new tank my boiler locks out even though my cooktop and gas dryer continue to work. My boiler is a 2 year old Weil McClain Evergreen Pro 155. Have had no problems with the boiler until I turned on the valve fir the new tank. Any ideas of what is going on?

Comments

  • rumn8r
    rumn8r Posts: 112

    More info: There is a manifold above the regulator on the original tank with propane lines going to two different locations. They used a tee to attach the new tank to the line that does not supply the boiler. Each tank has a high pressure regulator snd there are two low pressure regulators on the side of the house.

    HVACNUT
  • HVACNUT
    HVACNUT Posts: 7,825

    Seperate regulators on each tank then joined? Is there a third regulator where it goes into the house? Do you close the old tank before opening the new tank, or both open? The boiler is a lot more sensitive to pressure than a range or drier. Any elevation adjustments needed for the boiler?

  • Jamie Hall
    Jamie Hall Posts: 28,026

    What happens when you ony run the new tank, with the old one shut off? Or am I misunderstanding you and that is exatly what you are doing?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • rumn8r
    rumn8r Posts: 112

    Same result (boiler lock-out) if I have both tanks open or just the new tank. When I then switch back to the old tank it takes as many as 10 prepurge/ignition cycles to fire.

  • rumn8r
    rumn8r Posts: 112
    edited 2:33AM

    Each tank has a high pressure regulator (10 psi, I think) and there are low pressure (1/2 psi, I think) where they enter the house.

    I open the new tank then close the old tank.

    Everything has been working fine until we added the new tank.

    The cooktop and gas dryer work with each tank alone and with both open.

  • mattmia2
    mattmia2 Posts: 18,476

    does the dryer prove flame or does it just prove that the ignitor is on? the range proves nothing unless you're using the oven. the boiler will prove flame usually through flame rectification so the flame needs to be a certain size or bigger.

  • rumn8r
    rumn8r Posts: 112

    The dryer heats up. All range burners have flame. Electric oven.

  • mattmia2
    mattmia2 Posts: 18,476

    do the flames on the cooktop lift or flutter?

    my point is that the dryer and cooktop will be pretty tolerant of gas that is contaminated with say air because they don't prove flame directly i don't think.

  • rumn8r
    rumn8r Posts: 112

    flames seem fairly steady: mostly blue with some yellow

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,393

    So it sounds like the gas outlet on the new tank if feeding into one of two pipes leaving the original manifold going into the house. Andthey teed into the pipe that does not feed the boiler?

    Do I have this right?

    Can't really say why it doesn't work but maybe the prv is not letting the new line back up into the manifold so it won't feed the boiler.

    The fix is to have the new tank feed the manifold instead of one of the manifold outlets. Or ty both tanks together and then feed the manifold. Pictures might help.

  • 109A_5
    109A_5 Posts: 4,803

    I am also thinking air in the new tank. Maybe if there is a time when you can disable the boiler and just use the cooktop and gas dryer to help purge the air out.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • rumn8r
    rumn8r Posts: 112
    edited 4:17AM

    Yes you have it right.

    what is prv?

    Having the new tank feed into the manifold was the original intent but they cut through the propane line when excavating for the new tank and decided to add the new tank there with a tee.

    If they added it to the line on the other side that fed other things including the boiler it might not be a problem.


    i will add photos tomorrow.


    I thought there might be air in the new tank so I turned the dryer on for a 40 minute cycle before re-starting the boiler but it didn't work.

    They installed the tank nearly 5 months ago and filled both tanks to 80%. The new tank is still at 80% but the old tank is at 45%. I checked a couple days ago and found that they forgot to turn the new tank on after they installed it. When I turned it on is when all this started.