Any major cons/risks of a gas conversion burner?
I have a Smith 8 series boiler in good condition, only 13 years old, maintained regularly. Are there any major cons to putting a gas conversion burner (like a Carlin EZ Pro) on it to extend its life while also switching the gas? Many plumbers have said it causes more service issues longer term, and that it's extremely loud.
Comments
-
Not so much with a boiler.
The problems you sometimes encounter with gas conversion burners are more commonly associated with warm-air furnace heat exchangers.
A heat exchanger in a warm-air furnace has what is sometimes referred to as a thermal memory. Over the years, the repeated expansion and contraction of the metal establish a pattern of movement in the heat exchanger. When you change the burner from oil to gas, the flame temperature and flame pattern are different. This changes how and where the metal expands and contracts.
If the oil burner has been operating in that furnace for 10 years or more, the new flame pattern may cause the metal to flex in different locations than it has become accustomed to. In some cases, this can result in a heat exchanger developing a failure within a year of installing the new burner.
A boiler is a different situation. Because there is water on the other side of the cast-iron or steel heat-transfer surfaces, the difference in flame temperature is not nearly as significant a factor. The water absorbs the heat, and the boiler's operating temperature is controlled by the high-limit aquastat, which shuts off the burner when the set temperature is reached.
I have installed gas conversion burners in boilers that were 50 years old, and those boilers continued to operate without problems for many years after the new burner was installed.
The apprehension some plumbers and installers have about installing conversion burners often comes down to their lack of familiarity with the process. They may simply not have the experience or confidence to perform the installation properly.
My suggestion is to get another opinion from someone who has actual experience installing gas conversion burners. I think you will get the answers you are looking for from a contractor who is familiar with this type of work.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
-
If you have a stainless steel chimney liner you are good to go regardless of fuel choice. A power venter is fine as well.
I don't see very much in the way of disadvantages to it. I've worked on and set up several conversion burners and they never have any problems. Like Ed said I wouldn't recommend it for forced air furnace, even though I have seen some really old Thermopride furnaces work fine with a EZ Gas burner. No problem with a boiler. Those Smith boilers are good quality and should work well with a conversion burner.
1 -
-
A few items to keep in mind.
If the boiler is piped improperly (steam or hot water) , the new gas conversion burner will not fix that.
The boiler, the smoke pipe and the chimney and chimney base should be cleaned.
i think code requires a double acting draft regulator on the smoke pipe. Some oil boilers only have the single acting type. Code may also require a spill switch at or near the draft regulator.
In NJ I believe the code requires that you take care of the oil tank (indoor or outdoor) and remove the oil lines.
If there is inadequate fresh air for combustion, the conversion burner will not fit that.
You will almost certainly need to run a new dedicated gas line from the gas meter to the boiler. In other words, don't tap that existing gas line that feeds the dryer and the water heater.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 135 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements