Taco ZVC- Pump off immediately?
I’ve been a loyal Taco relay control user for decades. I dont want to jump ship- I like green. I called Taco last week asking “how do I get the pump to shut off immediately”. We have a “thump” when the last zone valve shuts.
The Viessmann has the classic 10 minute (or so) post purge. I spoke with tech support and the Taco employee told me that there will still be a 5 or 10 second delay before the AUX pump outputs will de energize.
In other words, the thump won’t be dealt with. Either I didn’t communicate well of the new design isn’t good. What work around is there- install a separate SR501 paralleled into the low voltage end switch? Seems excessive
The previous Taco ZVCs had an end switch for the pump that worked very well
Comments
-
Looks like things may have changed at since the new owners took over? Looks like Hot Rod (Caleffi) may be getting some orders in the near future?
0 -
-
DJS why not kill the power to the pump when the call for heat ends? Seems basic but I'm just a tool guy
0 -
Wait, what? If you turn off a pump abruptly, without some form of shock absorption in the piping involved, it's going thump. Maybe louder. Maybe almost silent. But it is going to thump.
Makes absolutely no difference when. 5 seconds? 5 minutes? 5 hours? Close valve, thump. Turn off pump, thump (particularly it there is a check valve).
The Taco controller has no authority over the physics of fluid flow, so look elsewhere for you solution.
Edit to add: if you spool a pump down slowly, or close a valve slowly, that works — and that is something a controller might be able to accomplish, but that depends on the pump or valve design.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I just want the pump to shut off when the heat call ends.
1 -
Not familiar with the control, but looking at the instructions it looks like on startup thermostat opens a zone valve and delays boiler and circ operation, so the valve gets open.
On shutdown it looks like they keep pump on for post purge but the valve is shutting causing the thump. I don't see any way around this from what I have read.
There instructions say something like "more adjustments available in the mobile app"
Seems like if you switch the dip switch "master off" it eliminates the post purge but you need it on master for the control to work without expansion modules.
But that was just a quick read I could be way off on this.
0 -
How is it wired now? Your primary System pump that's staying on a bit too long, is that on Aux 1?
Did you try it on Aux pump 2 terminals? I've read that the aux 1 and aux 3 can stay energized a bit longer depending on what else is configured and what all was set up on the Bluetooth app for any post purge timers.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 135 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements