lowering the heat load reduced required SWT by ??
Options
hot_rod
Posts: 28,771
50,000 btu/ hr load Q-exisiting
70° inside ambient T-in
180°SWT T-De
Envelop upgrades reduced the load to 40,000 BTU/hr Q-new
70 + (40,000 ÷ 50,000) X (180-70)
70 +(.8 X 110)
70 + 88= 158° new required SWT
If you could lower the load to 36,000 BTU/hr required SWT of 149° would put you in to condensing temperature 129°. The system running a 20∆ (149°-20)= 129°
At design day.
With ODR outdoor reset you could hit the condensing mode sooner as outdoor increases above design.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream