lowering the heat load reduced required SWT by ??

Options
hot_rod
hot_rod Posts: 28,771

50,000 btu/ hr load Q-exisiting

70° inside ambient T-in

180°SWT T-De

Screenshot 2026-11-16 at 3.56.17 PM.png

Envelop upgrades reduced the load to 40,000 BTU/hr Q-new

70 + (40,000 ÷ 50,000) X (180-70)

70 +(.8 X 110)

70 + 88= 158° new required SWT

If you could lower the load to 36,000 BTU/hr required SWT of 149° would put you in to condensing temperature 129°. The system running a 20∆ (149°-20)= 129°

At design day.

With ODR outdoor reset you could hit the condensing mode sooner as outdoor increases above design.

Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream

Comments

  • mattmia2
    mattmia2 Posts: 18,436
    edited November 16

    of course Tde isn't really 180f, it is just something you pick so you can do the math without using calculus.