lowering the heat load reduced required SWT by ??
50,000 btu/ hr load Q-exisiting
70° inside ambient T-in
180°SWT T-De
Envelop upgrades reduced the load to 40,000 BTU/hr Q-new
70 + (40,000 ÷ 50,000) X (180-70)
70 +(.8 X 110)
70 + 88= 158° new required SWT
If you could lower the load to 36,000 BTU/hr required SWT of 149° would put you in to condensing temperature 129°. The system running a 20∆ (149°-20)= 129°
At design day.
With ODR outdoor reset you could hit the condensing mode sooner as outdoor increases above design.
trainer for Caleffi NA
Living the hydronic dream
Comments
-
of course T
deisn't really 180f, it is just something you pick so you can do the math without using calculus.0