I would be fine with that. You can max out the amount of recovery the AL35S can have if you use a larger boiler, however that is not necessary in most cases. There is only a small increase in recovery with the boiler size increase to 150,000 NET compared to the 97,000 NET provided by a ALTA 120.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
It comes down to how much flow you can get through the coil and the surface area of the coil.
If this is your tank? They rate that tank at 6 gpm, 99K boiler input 180 SWT.
6 gpm, 9' head, you probably would not need a 26-99? Unless you are trying to squeeze more performance form the tank?
An indirect is limited by the fact the coil sits in a puddle of stagnant, non moving, water.
A pumped plate HX like EK uses is about 5 times more efficient.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
What would the piping schematic for a pumped plate set look like ?
What type of tank is used, a buffer style?
0 -
i've considered adding a plate hx to my indirect so if there is flow from a demand the incoming cold water flows across the return water to the boiler and drives the delta up which will work great with a mod con. with a conventional boiler you have to be careful that it has enough output to keep the supply temps up so the boiler doesn't condense.
0 -
EK sells the complte package. Or build on with a plate HX and non ferrous, stainless or composite pump
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
so that is storing hot boiler water in a system side buffer tank and using that to heat dhw on demand with the plate hx, basically a tankless with a buffer.
0 -
I had this conversation with my Burnham rep. An Alta 120 would work just fine with an indirect. A 15-58 pump would be just fine. The big thing with an indirect is to add a mixing valve to the outlet of the tank. Don't just use the supplied aquastat to control the domestic hot water temp.
I did a job similar to this over the summer where I had to install a buffer tank because of micro zones and it had a 50 gallon indirect. If no heating zones are calling and it's just the domestic hot water usually it will draw off the buffer tank for a bit to temper the water. Then when the Alta turns on it always would condense . Using the adaptive control on the Alta is key vs using a outdoor reset sensor.
Owner of Grunaire Climate Solutions. Check us out under the locate a contractor section. Located in Detroit area.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 135 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 52 Job Opportunities
- 18 Recall Announcements