Component compatibility?

Options

Does a Burnham Alta 120b meet the criteria for satisfying an Alliance AL35SL's tank BTU and flow need s if the piping is 1 inch copper and the an Alpha 2 26-99 circulator is used?

bburd

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,996

    I would be fine with that. You can max out the amount of recovery the AL35S can have if you use a larger boiler, however that is not necessary in most cases. There is only a small increase in recovery with the boiler size increase to 150,000 NET compared to the 97,000 NET provided by a ALTA 120.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Posts: 28,766

    It comes down to how much flow you can get through the coil and the surface area of the coil.

    If this is your tank? They rate that tank at 6 gpm, 99K boiler input 180 SWT.

    6 gpm, 9' head, you probably would not need a 26-99? Unless you are trying to squeeze more performance form the tank?

    Screenshot 2026-11-15 at 9.00.12 AM.png

    Screenshot 2026-11-15 at 9.00.41 AM.png

    An indirect is limited by the fact the coil sits in a puddle of stagnant, non moving, water.

    A pumped plate HX like EK uses is about 5 times more efficient.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • hevysrf
    hevysrf Posts: 13

    What would the piping schematic for a pumped plate set look like ?

    What type of tank is used, a buffer style?

  • mattmia2
    mattmia2 Posts: 18,428

    i've considered adding a plate hx to my indirect so if there is flow from a demand the incoming cold water flows across the return water to the boiler and drives the delta up which will work great with a mod con. with a conventional boiler you have to be careful that it has enough output to keep the supply temps up so the boiler doesn't condense.

  • hot_rod
    hot_rod Posts: 28,766

    EK sells the complte package. Or build on with a plate HX and non ferrous, stainless or composite pump

    Screenshot 2026-11-15 at 1.01.42 PM.png

    Screenshot 2026-11-15 at 1.04.47 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • mattmia2
    mattmia2 Posts: 18,428

    so that is storing hot boiler water in a system side buffer tank and using that to heat dhw on demand with the plate hx, basically a tankless with a buffer.

  • I had this conversation with my Burnham rep. An Alta 120 would work just fine with an indirect. A 15-58 pump would be just fine. The big thing with an indirect is to add a mixing valve to the outlet of the tank. Don't just use the supplied aquastat to control the domestic hot water temp.

    I did a job similar to this over the summer where I had to install a buffer tank because of micro zones and it had a 50 gallon indirect. If no heating zones are calling and it's just the domestic hot water usually it will draw off the buffer tank for a bit to temper the water. Then when the Alta turns on it always would condense . Using the adaptive control on the Alta is key vs using a outdoor reset sensor.

    Owner of Grunaire Climate Solutions. Check us out under the locate a contractor section. Located in Detroit area.