nate379 Posts: 185
edited October 26 in Oil Heating

Aside from fairly expensive controllers, is there an easy solution to setting up 2 boilers?

Would something just as setting one to run 160-180* and the other 140-180* work? 1 boiler would run normally and the other would only kick on if water temp gets too low.

Heat load currently doesn't require 2, but in the future it may, especially if I do a heated parking pad (snow melt)

Forgot to mention, they are cast iron oil fired boilers, if that matters.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,372

    You can do that but you're wasting some fuel keeping the idle boiler hot. I have a drawing of a simple lead-lag system where you can run #1 boiler on lead (higher temp) #2 on lag (lower temp) or have them both on lead or both on lag. Of course, you can always shut 1 boiler off if you don't mind needing a back up.

    If you wan't the drawing I will look for it. You need 2 relays and 2 aquastats in addition to what you have and some wiring.

    GGross
  • hot_rod
    hot_rod Posts: 28,790

    A solar differential control would work nicely.

    Basically it has two sensors, two relay outputs.

    So if the first boiler cannot keep up it fires the second. It watches the first boiler and if it can catch up to the load it drops off the first.

    Temperatures and differentials are all adjustable. VS pumping is on board, basic data logging reads out on the screen.

    I like the Resol brand, but others are available. Resol still import through Canada.

    https://shop.modularhydronics.com/resol-deltasol-sl-solar-controller-full-kit-4-sensors

    Screenshot 2026-10-25 at 7.19.51 PM.png Screenshot 2026-10-25 at 7.19.21 PM.png Screenshot 2026-10-25 at 7.26.52 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • 109A_5
    109A_5 Posts: 4,790
    edited October 26

    The Tekmar 257 possibly could be utilized to do the boiler staging control. Since it does not have a demand input, the heat demand thermostatic control would have to interrupt the T-T to both boilers from the Tekmar 257 controller. The Tekmar 257's literature would have to be read, and understood to verify it will do what is actually needed for your application.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Posts: 4,790
    edited October 26

    You may be able to use the Tekmar 257 like this. (No Tekmar 257 to boiler T-T interruption needed, like above)

    When the 24 Volt relay is de-energized (no call for heat) the 820 Ohm resistor is connected to the Tekmar 257's sensor terminals so the Tekmar 257 thinks the water temperature is about 200 degrees shutting the boiler(s) down.

    When there is a call for heat the 24 Volt relay is energized connecting the Tekmar's normal sensor to the Tekmar 257's sensor terminals for normal boiler operation as per the Tekmar 257's programming.

    image.png image.png

    The 820 Ohm resistor is not critical, it just has to be a value that represents a temperature that is above the Tekmar 257's target temperature. The connections to the 820 Ohm resistor should be very secure, no poor quality crimps.

    https://www.watts.com/dfsmedia/0533dbba17714b1ab581ab07a4cbb521/42659-source/070-dl-06

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • nate379
    nate379 Posts: 185

    Those are all expensive controllers.

  • nate379
    nate379 Posts: 185

    That's ok, the fuel is free. If anything, I actually get more than I can use…. can easily get 5000+ gallons a year if I wanted.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,372
  • nate379
    nate379 Posts: 185

    Can you explain a bit? How is that 3 way switch adjusting the boiler temp setting?

  • 109A_5
    109A_5 Posts: 4,790

    I would say this is the difference. The 3-Way switches just do the manual selection. BTW don't price the suggested relays, I bet you won't be happy.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,372

    There are two three-way switches one for each boiler. All the switch does is send the burner starting circuit through the lead (hi temp) relay or through the lag (low temp) relay. So if you have 2 aquastats on the header one set at 140 lag and 1 set at 190 lead you can run both boilers on lead, or both boilers on lag or #2 boiler lead and #1 boiler lag or vise versa just by using the switches.

  • hot_rod
    hot_rod Posts: 28,790

    Electronic setpoint are about a cheap as you can get

    Two of these and two relays?

    May as well buy a tekmar or solar control

    IMG_3545.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    nate379
  • nate379
    nate379 Posts: 185

    I found a used Tekmar 261 for about $200 so ended up grabbing that. The switches and relays maybe could work with cheaper relays? I'm not sure. The ones listed didn't have much available online, the ones I found were around $150 each.

    It's supposed to be smart and switch between the 2 boilers as well as know when to run 1 or 2… I guess.

    I'm assuming it's smart enough that if one unit shuts off on safety or I turn it off for maintenance that it will run the other one and not go crazy.

    The used Tekmar didn't come with the temp sensor. Is there anything special about the Tekmar one that is around $50 vs a regular 10k one that I can buy for a few dollars each?

    https://www.ebay.com/itm/267389643531?chn=ps&norover=1&mkevt=1&mkrid=711-117182-37290-0&mkcid=2&mkscid=101&itemid=267389643531&targetid=2450249296795&device=c&mktype=pla&googleloc=9033936&poi=&campaignid=24181853928&mkgroupid=204814195412&rlsatarget=pla-2450249296795&abcId=10813847&merchantid=108350853&gad_source=1&gad_campaignid=24181853928&gbraid=0AAAAAD_QDh9m3jlP6HmW35KajhhjtFrUw&gclid=CjwKCAjwuobXBhBXEiwAYUaIlT05xa6RpZAym8QVglPPfDWvPLbHcxL4QuFK0XIFshZp46q2LaBBLxoCy0oQAvD_BwE

  • 109A_5
    109A_5 Posts: 4,790

    Maybe this will add a bit of clarity to the drawing.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Posts: 4,790

    Appears the B-Constant or Beta is different. You would have to compare the resistance curves to see if the difference is acceptable to your application.

    image.png

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    nate379
  • 109A_5
    109A_5 Posts: 4,790

    " The switches and relays maybe could work with cheaper relays? I'm not sure. "

    The Honeywell RA845A has its own 120 to 24 VAC transformer in it.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • hot_rod
    hot_rod Posts: 28,790

    use the tekmar sensor

    No harm in making an offer This shows best offer and free shipping

    IMG_3547.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • 109A_5
    109A_5 Posts: 4,790
    edited October 29

    Apparently the material NTC thermistor sensors are made with is very manufacture specific, standards are limited.

    In the range you are probably going to use it in, it may not matter much. Or you could use a second opinion for the actual temperature.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    nate379
  • Steve214
    Steve214 Posts: 23

    If the fuel is free, why bother???

  • nate379
    nate379 Posts: 185

    Makes sense. Maybe folks in the industry have a better source for them, but my searching was coming up with around $150 for each.

  • nate379
    nate379 Posts: 185

    Thanks for the info on the thermistors. I wasn't sure what the 3892 meant.

    I did a bit of digging and using the 3950 when the controller is expecting the 3892 would mean

    Controller reads 140*, actual temp about 139*

    Controller reads 160*, actual temp about 158*

    Controller reads 180*, actual temp about 178*

  • nate379
    nate379 Posts: 185

    I found that one as well, but they won't ship to me.

  • hot_rod
    hot_rod Posts: 28,790

    You should always

    Screenshot 2026-10-29 at 12.22.49 PM.png

    use the manufacturers sensor

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    nate379
  • nate379
    nate379 Posts: 185
    edited October 31

    I'm not sure what you're asking. The purpose of the controller in my case is so they aren't fighting each other or short cycling.

    Maybe it's doable without? Didn't seem to be the case in this thread or from online reading.

  • hot_rod
    hot_rod Posts: 28,790

    It depends a bit on how they are piped.

    Are they piped parallel of with primary/ secondary?

    Generally you wouldn't run flow through an unfired boiler. So they need to be disconnected in the piping to really benefit from staging.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream