Controlling dual boilers
Aside from fairly expensive controllers, is there an easy solution to setting up 2 boilers?
Would something just as setting one to run 160-180* and the other 140-180* work? 1 boiler would run normally and the other would only kick on if water temp gets too low.
Heat load currently doesn't require 2, but in the future it may, especially if I do a heated parking pad (snow melt)
Forgot to mention, they are cast iron oil fired boilers, if that matters.
Comments
-
You can do that but you're wasting some fuel keeping the idle boiler hot. I have a drawing of a simple lead-lag system where you can run #1 boiler on lead (higher temp) #2 on lag (lower temp) or have them both on lead or both on lag. Of course, you can always shut 1 boiler off if you don't mind needing a back up.
If you wan't the drawing I will look for it. You need 2 relays and 2 aquastats in addition to what you have and some wiring.
1 -
A solar differential control would work nicely.
Basically it has two sensors, two relay outputs.
So if the first boiler cannot keep up it fires the second. It watches the first boiler and if it can catch up to the load it drops off the first.
Temperatures and differentials are all adjustable. VS pumping is on board, basic data logging reads out on the screen.
I like the Resol brand, but others are available. Resol still import through Canada.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The Tekmar 257 possibly could be utilized to do the boiler staging control. Since it does not have a demand input, the heat demand thermostatic control would have to interrupt the T-T to both boilers from the Tekmar 257 controller. The Tekmar 257's literature would have to be read, and understood to verify it will do what is actually needed for your application.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
You may be able to use the Tekmar 257 like this. (No Tekmar 257 to boiler T-T interruption needed, like above)
When the 24 Volt relay is de-energized (no call for heat) the 820 Ohm resistor is connected to the Tekmar 257's sensor terminals so the Tekmar 257 thinks the water temperature is about 200 degrees shutting the boiler(s) down.
When there is a call for heat the 24 Volt relay is energized connecting the Tekmar's normal sensor to the Tekmar 257's sensor terminals for normal boiler operation as per the Tekmar 257's programming.
The 820 Ohm resistor is not critical, it just has to be a value that represents a temperature that is above the Tekmar 257's target temperature. The connections to the 820 Ohm resistor should be very secure, no poor quality crimps.
https://www.watts.com/dfsmedia/0533dbba17714b1ab581ab07a4cbb521/42659-source/070-dl-06
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Those are all expensive controllers.
0 -
That's ok, the fuel is free. If anything, I actually get more than I can use…. can easily get 5000+ gallons a year if I wanted.
0 -
-
Can you explain a bit? How is that 3 way switch adjusting the boiler temp setting?
0 -
There are two three-way switches one for each boiler. All the switch does is send the burner starting circuit through the lead (hi temp) relay or through the lag (low temp) relay. So if you have 2 aquastats on the header one set at 140 lag and 1 set at 190 lead you can run both boilers on lead, or both boilers on lag or #2 boiler lead and #1 boiler lag or vise versa just by using the switches.
0 -
Electronic setpoint are about a cheap as you can get
Two of these and two relays?
May as well buy a tekmar or solar control
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I found a used Tekmar 261 for about $200 so ended up grabbing that. The switches and relays maybe could work with cheaper relays? I'm not sure. The ones listed didn't have much available online, the ones I found were around $150 each.
It's supposed to be smart and switch between the 2 boilers as well as know when to run 1 or 2… I guess.
I'm assuming it's smart enough that if one unit shuts off on safety or I turn it off for maintenance that it will run the other one and not go crazy.
The used Tekmar didn't come with the temp sensor. Is there anything special about the Tekmar one that is around $50 vs a regular 10k one that I can buy for a few dollars each?
https://www.ebay.com/itm/267389643531?chn=ps&norover=1&mkevt=1&mkrid=711-117182-37290-0&mkcid=2&mkscid=101&itemid=267389643531&targetid=2450249296795&device=c&mktype=pla&googleloc=9033936&poi=&campaignid=24181853928&mkgroupid=204814195412&rlsatarget=pla-2450249296795&abcId=10813847&merchantid=108350853&gad_source=1&gad_campaignid=24181853928&gbraid=0AAAAAD_QDh9m3jlP6HmW35KajhhjtFrUw&gclid=CjwKCAjwuobXBhBXEiwAYUaIlT05xa6RpZAym8QVglPPfDWvPLbHcxL4QuFK0XIFshZp46q2LaBBLxoCy0oQAvD_BwE
0 -
use the tekmar sensor
No harm in making an offer This shows best offer and free shipping
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Apparently the material NTC thermistor sensors are made with is very manufacture specific, standards are limited.
In the range you are probably going to use it in, it may not matter much. Or you could use a second opinion for the actual temperature.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
If the fuel is free, why bother???
0 -
Makes sense. Maybe folks in the industry have a better source for them, but my searching was coming up with around $150 for each.
0 -
Thanks for the info on the thermistors. I wasn't sure what the 3892 meant.
I did a bit of digging and using the 3950 when the controller is expecting the 3892 would mean
Controller reads 140*, actual temp about 139*
Controller reads 160*, actual temp about 158*
Controller reads 180*, actual temp about 178*
0 -
I found that one as well, but they won't ship to me.
0 -
You should always
use the manufacturers sensor
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I'm not sure what you're asking. The purpose of the controller in my case is so they aren't fighting each other or short cycling.
Maybe it's doable without? Didn't seem to be the case in this thread or from online reading.
0 -
It depends a bit on how they are piped.
Are they piped parallel of with primary/ secondary?
Generally you wouldn't run flow through an unfired boiler. So they need to be disconnected in the piping to really benefit from staging.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 135 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements