MoM Vent Failures - First Fire Up for the Year
This has been happening the past three years. I fire up the boiler for the first time and let it run for a while to check out the system. Make sure the main vents open, make sure the radiator vents open, system heats evenly, etc.
For the past three years I've had a couple dead Maid O' Mist vents. This year it was two of them. I let the system run for a while and go around and check for even heat on the radiators. Two of the radiators were cold as ice.
Gave the vents a couple whacks…nothing. Took the orifice off the top…nothing.
Took the vent off and it wouldn't make any rattling noises when shaking. I put a couple "previously dead" spare MoM vents on and got the radiators back up and running.
Last year I boiled previous two years of dead MoM vents in vinegar and then water a few times to try and clean them out. Lots of junk came out and they rattled again so I kept them as spares. They are back in service and working for now.
This seems to happen every year…a couple dead MoM's. I'm considering changing to Gorton.
This happen to anyone else? My boiler runs great with no issues (other than being oversized) but it seems to keep happening.
Comments
-
what is your pressure troll set too?
0 -
I've got a Vaporstat with a pressuretrol as a backup. Vaporstat cuts in at 16oz of pressure with about a 12oz differential.
My boiler is 50% oversized so it does cycle on pressure. It is also 40 years old so I try to keep the pressure as low as possible to help it live its longest life.
It just seems that every year I am replacing 1-2 MoM vents. …..and I've only got 6 radiators.
0 -
Yes they fail. Gorton fail also. Which one fails more? No one can say. Try Gorton and see if they are better for you.
NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements