also expansion tank charge is good 12 psi. Was unscrewed from system and checked. I want to instal a couple of pressure gauges to drain ports next check, then bleed, and check again
0 -
Hi guys, I just got back after a trip and have started working on the boiler again. I got the lower pump oriented correctly. Expansion tank was removed and verified working (and at right pressure). Installed three garden hose pressure gauges, one before the pump that is having troubles one after pump (before manifold loops) and one on return of manifold. When he changed pump must of lost some pressure, the boiler says at 11.4 psi, however all three gauges read 9 psi. When I run pump with that valve that’s causing issues partially closed, the first gauge before pump reads 9, gauge after pump reads 15psi, and gauage after loops reads 9psi. This is running just the pump (no heat). I also purchased a pump, and have more glycol here so I can attempt to purge it. Thanks for all the help so far, just figured I would submit more of what I’ve done recently.
0 -
Sure the valve handle isn't in the wrong position on the shaft?
1 -
I can get all 4 loops virtually closed (via gauges) and they still show no flow if the valve directly after pump is fully open. Valve handle came pre installed, has stops so you can only rotate it 90 degrees, a month or so ago when plumber had pump off, it was bottomed out against stop and did not leak therefore i would think if I rotate 90 degrees into other stop that would be fully open?
0 -
You could tell for sure by removing the circ and looking into the flange.
0 -
yeah, balanced manifold via a guide now I hear water trickling in returns, assuming air in lines meaning, gonna bleed it
0 -
Faulty check valve in floor circ port ? (or debris caught behind it)
Or did you already verify that..
30+ yrs in telecom outside plant.
Currently in building maintenance.0 -
got the boiler fixed.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements