  • hot_rod
    hot_rod Posts: 28,329
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Evan456
    Evan456 Posts: 17

    It is 30% pre mixed Fernox glycol.

  • hot_rod
    hot_rod Posts: 28,329

    if you are seeing .7-.9 gpm per loop what makes you think ot is not working correctly?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Big Ed_4
    Big Ed_4 Posts: 3,583

    My guess this system needs a good purge ….

    There was an error rendering this rich post.

  • Brent H.
    Brent H. Posts: 184

    Have you checked to make sure there isn’t a manufacturing issue with the ball valve? Could you actually be opening it when you think you are closing it a bit? Highly unlikely but weird issues sometimes have weird causes😀

  • Evan456
    Evan456 Posts: 17

    hot rod why is a ecm pump a bad idea? The only reason I think the system isn’t working well is because why else would the valve have to be partially closed? Brent I thought same thing initially is ball valve wrong but it has pegs on it so u can only rotate 90 degrees one way and if u shut it off it doesn’t leak when the pumps off so if closing works I’d assume being open works?..

  • hot_rod
    hot_rod Posts: 28,329

    There is nothing wrong with the pumps you have. If you changed it 3 times and the problem persists it’s not the pump.
    Keep looking, you have 10 or so suggestion's for things to check, make a list and check them off

    There is no way that closing off a valve increases flow,

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • 109A_5
    109A_5 Posts: 4,470
    edited 4:53AM

    Maybe just move it.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • plumbworker
    plumbworker Posts: 30
    edited 5:47AM

    Whats the voltage measurement at the pump output contacts when the pump stops working? Navien leaves much to be desired especially on the control side..