Gas pipe sizing
My shop building currently has a 120,000 BTU boiler for floor heat.
I'm adding an 80,000BTU hanging heater as a backup as to supplement. I'm out of town about 60% of the year and have had the boiler go down before, which became kind of an emergency. Shop has plumbing, plus of course the floor heat, none would be good to freeze.
Currently the gas meter hangs on the building, 1" pipe goes through the wall then it 90*s and turns into 3/4" for about 25ft to feed the boiler. Figure around 40ft "pipe length" when figuring Ts and elbows between meter and boiler.
If my reading is correct, to add the 80k unit, 1" will be suitable. (yes?)
Trying to future proof this a bit. Plan to install a 10-14k home backup genset, and in some years also feed a house (yet to be built). My math pencils out to total of 740,000 BTU if everything would be on and wide open.
The feeds to the gen set and future home would branch off near the meter. So picture meter and then a 4 branch manifold. Shop, generator, house and test port (required by gas company)
Would the pipe for the shop still be adequate at 1"?
Gas setup is .5" W.C. I can go to 850 cfh on the meter and rate I have. Above put me into commercial. Or I'd need to do 2 gas meters, which would be more expensive than 1.
  • ChrisJ
    ChrisJ Posts: 17,780
    740,000 btu....
    I don't have my charts with but at 40' that's gotta be at least 1.5" and quite possibly 2" pipe for 0.5" drop.
    hot_rod Posts: 28,799
    edited October 11
    A drawing would help. 25’ to the boiler, how far beyond that is the unit heater?
    If the generator set is at the meter, just that section sizes for total of 3 loads
    https://www.beckettcorp.com/tutorials/burner-tutorials/gas-pipe-sizing-tutorial/
    EdTheHeaterMan Posts: 13,035
    So far I can tell you that 3/4" is not enough for the shop based on 40 feet from the manifold to the appliances. so make that 1" until you branch off to each appliance. stick with 1" to the boiler and reduce to 3/4" within 5 feet of the boiler. You can drop to 3/4" where you branch off the the unit heater. That assumes that you will not be longer than 50 feet total from the manifold to the unit heater. You may be able to drop to 3/4' to the boiler but you must be sure that there is less than 60 feet total equivlent length from the manifold to the boiler. Stick with 1" to be safe.
    I need three details to size the actual runs and the manifold to the meter piping
    1. Meter to manifold: How many feet of pipe, including the route around the building?
    2. Manifold to shop: How many feet of pipe, and is it all black steel?
    3. Gas and pressure: Is it natural gas at typical low pressure (about 7 inches water column), or a higher-pressure system with a regulator?
    4. If you have a higher pressure from the meter to the future building then you can use smaller diameter piping.
    5. Think about a higher pressure like 1.5 to 2 PSI from the meter to the future building. then add a pressure regulator down to 7"WC at the building entrance.
    6. Same for the shop. Start at 2 PSI with a regulator at the entrance to the shop.
    Sometimes the gas company does not let you have higher pressure after the meter.
  • nate379
    nate379 Posts: 185
    edited October 11
    Meter is on the building. Manifold would be at the meter. 1" in the shop, never said 3/4" other than that is the existing pipe.
  • nate379
    nate379 Posts: 185
    Drawing. Sorry not a good drawerer, but gets the idea across, least to me me it does. House and gen set don't exist now, so hard to say exact figures.
    Will the new building piping start at the manifold and go to the new building at the lower pressure? You will need bigger pipes. If the gas company will allow higher pressure, then you can use smaller pipes with a second stage regulator at each termination.
    The second stage regulators will drop the pressure from 2 PSI to 7" WC where you enter the building and just before the generator. You can use smaller pipes for the 2 PSI Gas.
    ChrisJ
  • nate379
    nate379 Posts: 185
    edited October 11
    It's possible to do 2psi, though don't think I can do it now based off of speculative work. I have to prove it's required. Also from what I'm seeing, all the piping would have to be done by a licensed plumber and get signed off by gas company. Where std setup, they just inspect the meter through the wall and it's on you after that.
    I suppose either way would regulate down before the shop, so piping would need to be same size for the 2 heaters I'm dealing with now.
    2" burial line is fairly cheap, so not sure it would pencil out $$ wise to deal with the 2psi. That's a future me problem I guess!
    EBEBRATT-Ed Posts: 21,379
    @nate379
    Make the 4 port manifold at the meter make that 2". Leave the tee for the house and tee for the gen (future) at full size 2" because you don't know the pipe size yet.
    Off the manifold run 3/4" to the boiler and 3/4" to the new gas heater. If the heater and boiler are coming off the same manifold branch use 1" up to where they split.
    Obviously the meter has to be sized for the entire load although the boiler and heater will probably not run at the same time.
  • nate379
    nate379 Posts: 185
    edited October 12
    Boiler and heater likely will run at the same time. Like if the shop door is open, or something cold is pulled in and it cools down the building. It's not the arctic, like where I work, but we do have a good period of time each year that is around -25*.
    The pipe coming in the shop is 1" and reduces to 3/4". 3/4" runs to each heater? The 80k heater is fairly close to where that 1" comes in, just the pipe will run to near the ceiling.
    use the chart to get in the ball park, 3/4” can handle 152,000 at 30’ length
    So start with 1”, run to two loads with 3/4
    Mine says 3/4 will do 198cfh @30'
    Either way. They way I laid it out in my previous post should work fine. 2"@" manifold to handle the entire load of 740 located at the meter. 1" into the building will feed the boiler and the heater with 2 3/4" branches. Gen and house to be added at a later date.
    nate379
  • ChrisJ
    There's charts for both 1/4" drop and 1/2" drop commonly used for 7" systems.
    I assume Hot Rod's is 1/4" but it doesn't say.
    Fittings also need to be included past a certain amount and don't forget "gas cocks" if used aren't full port.
    Every code I have seen allows a 1/2" PD.
    mattmia2 Posts: 18,462
    if i am readign the code correctly, it allows the pressure drop to be delivering the rated inlet pressure at the appliance. if you have 6" wc at the meter outlet in most cases you have more like 1" wc pressure drop to work with.
    most of the sizing charts include some number of fittings although in the 80 years of them being reproduced in new versions of books and the code a lot of them have lost the footnotes with the calculations that were used for the chart. You can always do it with the formula in the code too.
    It might make more sense if you have enough pressure at the street to get a 2 psig service and put regulators at the groups of distribution equipment. 3/4" could handle the whole load, each of the branches could probably be 1/2"
  • ChrisJ
    edited October 12
    Yeah, I agree with Matt regarding code.
    If I remember correctly, they want the minimum pressure required by the appliance available at the appliance at all times. Or, something along those lines. I don't recall any code mentioning pressure drop.
    I used the 0.25" charts in my house because they give me 6" after the regulator, but before the meter. I also used full port NG rated ball valves anywhere there was a decent amount of volume and avoided street ells.
    Depends on the OPs location. In MA. and some other places 2psi is not allowed inside the house. 12" wc or 1/2 psi is max. If the OP only has 5" wc I kind of doubt he is on a HP system
  • ChrisJ
    Which is even more reason to go with the 0.25" drop chart.
    I thought in MA you could get 2 PSI in a house if you had approval from someone, tho I can't remember who that is?
    Never heard of 2psi in a house in MA.
    The code in MA is that everything starts off assumed to be low pressure (1/2 psi or less). If low pressure will not feed the load due to excessive pipe size needed, or the equipment needs more pressure, or a large building etc then you have to get "special Permission". In the past you had to go to Boston with a PE stamped drawing to get permission. A few years back they relaxed the rules and now the local inspectors make the decision but AFAIK no HP gas (over 1/2 psi) allowed in a house. Still need a PE stamped drawing I think.
    nate379