1 pipe steam radiator sludge
Options
NotSoYeung
Posts: 1
hi guys,
I'm new here, but been a service technician for a few years, got more things to learn.
I have a 11 radiator 1 pipe steam boiler system, I have been incrementally improving upon it, mostly from information here. Below is what I have installed.
anyway, my current problem is dealing with banging noises. it's almost like a drum roll banging noises at a few radiators.
Recently, upon removing 3 radiators, ( install flooring under the radiator), I see a large buildup of scale (it feels as solid as the cast iron) inside one radiator. Presumably this can cause a pocket of water and cause hammering. is there any chemical I can use to soften this scale/sludge for easier removal?


I'm new here, but been a service technician for a few years, got more things to learn.
I have a 11 radiator 1 pipe steam boiler system, I have been incrementally improving upon it, mostly from information here. Below is what I have installed.
anyway, my current problem is dealing with banging noises. it's almost like a drum roll banging noises at a few radiators.
Recently, upon removing 3 radiators, ( install flooring under the radiator), I see a large buildup of scale (it feels as solid as the cast iron) inside one radiator. Presumably this can cause a pocket of water and cause hammering. is there any chemical I can use to soften this scale/sludge for easier removal?


0
Comments
-
did you receive any answers? Even one?
0 -
unless the radiators hav uvusually narrow passages that isn't your problem.
0 -
Pipe pitch elsewhere near the radiator causing water to puddle in the pipe.
A magnet would tell you if the " large buildup of scale " is actually cast iron.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
- Please be sure to use a bubble level on each radiator to check it for adequate slope back to the main.
2 please check all the steam feeder pipes for adequate slope back to the boiler to allow drain back of the condensate back to the boiler.
0 -
- Failed valve gasket falls down and blocks water draining out of rads.
- Pitch of pipes near radiator.
Ethical Paul has numerous videos that show that radiator pitch isn't that important. It might only matter with very small inlets.
»»» See my steam heat YouTube videos:
https://www.youtube.com/@HeatingBlog1
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements