where should cold water feed be tied into boiler and recirc line-

this is existing system how water backing up into cold feed

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,014

    Maybe put a check valve on the cold.

  • Larry Weingarten
    Larry Weingarten Posts: 4,194

    Hi, I'd follow Ed's advice and add an expansion tank in the cold, downstream of the check. 😉