Weil McLain EG Piping Question

Options
saias
saias Member Posts: 21

WM installation has this notice:

"Steam supply must be on same end as controls. Return may be from either end."

See page 17 in their manual - https://www.weil-mclain.com/wp-content/uploads/EG-PEG-Series-6-Boiler-Manual-Web-Version.pdf

What do they mean by supply? The riser from the boiler or the supply takeoff from the header?

The Williamson manual, which looks like a photocopy of the WM manual, does not have this notice.

Answers

  • Jamie Hall
    Jamie Hall Member Posts: 27,769

    steam supply is the riser. The diagram is pretty clear…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,970

    The riser from the boiler

    Mad Dog_2