Lochinvar nkc199
Installer hooked up circulator direct with WAGO so it runs constantly. I dont see where circulator connects inside to boiler.thought about using taco relay controller externally. Heat and combi hot water works but not correct
Thanks
Comments
-
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
the combis have an internal circ that is factory wired
Is it piped primary secondary? A loop pump snd zone pumps may need to be wired
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Schematic shows brown wire no brown in bundle to lower junction box. Purple but no brown.
0 -
The contractor who installed this four years ago venting was two edge, emmanuel says three edge had a natural gas orifice. Its propane. Gasoline was too small for the run from the regulator I had to put a max attrol regulator there to boost the pressure. Gas company came out to do a tune up on it. A 1000 parts per million co should be like 20. My neighbor's an hvac guy. He got it all dialed in for me now. But I just noticed that the circulators running all the time
0 -
You can use the purple (system pump) wire. Do you have only one pump on the heating circuit?
If the pump is more than 2 amps, you must isolate with a relay.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Yes 2 zones one external pump
0 -
The way you wire it depends in how it is piped. How many pumps?
In any case all the pumps should shutdown if there is no heat or DHW call.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I guess i can call for heat and ck if purple energized. Schematic shows purple going to pump also
0 -
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 123 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements