Choosing Pumps for Monoflow Hydronic Heating System
Background information:
I previously posted asking for suggestions on how to split my monoflow-plumbed boiler into more zones here:
I’m getting around to doing the work, and I’m trying to figure out what I should do for pumps.
The big zone currently has a Bell and Gossett Series 100 pump. The plumbing is a ~35 foot run of 1-¼” copper (to the far end of the house) where it splits into two 1” runs, about 60’ long each going around the perimeter of the house back to the boiler. Each of these runs serves 5 convectors (3 on first floor and 2 on second floor) which are fed by ½” piping fishing from the monoflow tees which are at the basement ceiling height.
The zone that was added to the big zone at some point (the room is an addition) is plumbed in ¾” with monoflow tees to two convectors. There is about 70’ of pipe with about 10 elbows in the zone.
The existing basement zone has a Taco 110-338. This zone has ¾” piping and is series plumbed to two convectors in the basement. There is about 120 feet of piping in this zone, and about 12 elbows.
Questions:
  1. Is the Grunfos Alpha 15-58F (link https://www.supplyhouse.com/Grundfos-92603115-ALPHA-15-58F-Smart-ECM-High-Efficiency-Circulator-Pump-with-Optimized-Setpoint-Control) a good choice for replacing the Taco 110-338, and for putting on the newly split zone? This pump is attractive to me because it can show head and flow, and the output can be programmed. I cannot find a pump curve for the 110-338 to see if I can run the 15-58F at the same point.
  2. Would this same 15-58F be crazy to try out on the big zone too? I know that the B & G Series 100 is a much bigger pump, but I also think that the zone could be over-pumped as is, as my heat calls were not particularly long last winter, and the heat was calling a maximum of 26minutes/hour on the coldest day of the year. I really like the idea of having common pumps that can be programmed. And if one went bad, then a less important zone (the basement) pump could be easily swapped over to the more important zone.
    hot_rod Posts: 28,699
    The B&G and 110 are similar pumps. Sometimes considered high flow, low head circulators.
    How many gpm do you need. The 15-58 will not run out to the gpm of theses two.
    Screenshot 2026-09-11 at 12.26.21 PM.png Screenshot 2026-09-11 at 12.27.03 PM.png 15-58.png
    sre92
    EBEBRATT-Ed Posts: 21,328
    Don't know if I got this right:
    Basement zone take out taco 110 and install a Grundfoss 15-58F. Yes that looks ok to me.
    So the zone with the B& G 100 does an existing split monoflow zone which you want to make two zones?
    Is the existing zone that was added getting its own pump or staying on 1/2 of the B & G zone?
    You have to be a little cautious with Monoflow. They always seem to take more pump than they should.
  • sre92
    sre92 Posts: 21
    Thanks for finding that curve for me! Maybe adding the -338 on the model number was messing up my results. It seems like way too high flow of a pump for a 3/4" pipe! I would guess that it was originally on the main zone, and was switched over at some point.
  • sre92
    sre92 Posts: 21
    Here's a link to a diagram of the system as it exists. https://us.v-cdn.net/5021738/uploads/MD4E42AR8SSK/heating-system-existing.png
    So the big zone was originally for the whole main house. It does a split which I think may be unusual. At some point not long after the house was built, a small addition was added, and the heat for that got scabbed onto the monoflow zone. There are balance valves to make sure all legs of the single zone get flow. I want to remove the "scab" from the main zone, and add a pump so that it can be its own zone.
    So 1 circ for the basement
    1 circ for the existing monoflow-the scab zone- this zone will stay as a split loop
    1 circ for the scab zone.????????????
    I would use the 15-58FC (1)for the basement zone and also (1) for the "scab" zone.
    I would find a circ that matches the B & G 100 (that was the original circ) for the big zone. That is the "safe choice" I doubt the 15-58FC would pump the monoflow tees very well.
    hears the thing.
    The monoflow system was designed for a certain flow. Even if it is more flow than it needs the monoflow tees need that flow to distribute the gpm to the rads effectively
    JMHO
    those two pumps , the series 100 and the 110 are known as flat curve pumps . They are ideal for zone valved systems
    Pumps like to run in the middle of their curve for best efficiency and long life
    So about 15 gpm, and 6-8’ head
    If the design was around a 20 delta, estimate 15 gpm= 150,000 btu/ hr
    ideally you want to know
    Type of fluid
    Required gph
    Head
    To size a circulator
    I would shop for an ECM style for efficiency snd a lot of adjustability
    There are energy rebates available in some areas for using ECM circs
    Www.dsireausea.com
    is where you find incentive $$
  • sre92
    sre92 Posts: 21
    I've completed the plumbing, and I bought (2) Grunfos Alpha 15-58F since there was some consensus that they would probably work for the addition (piano room in the diagram) and the basement zone. Here's a diagram of the new plumbing for clarity. The working fluid is water.
    I have installed one 15-58F on the addition. I also installed one temporarily on the main zone. I looked at each convector with a thermal camera, and they look fairly even. I also collected some flow/head data from the app, though I don't know how accurate it is. It is not as linear as I expected. Here is a plot:
    If this data is accurate, it looks like the 15-58 is pumping more than the B&G 100 would pump, since it is a low-head pump:
    Questions:
    1. Would you trust the data from the 15-58?
    2. Would you keep the 15-58 on the main zone?
      1. if no, what would you install?
    You have a lot of adjustability with those circulators.
    When you take readings, especially temperature, you want the system to reach thermal equilibrium.
    All hydronic systems are going through a transient condition until the supply temperature and return temperature stabilized, neither rising or falling. At that point the radiators are moving all the boiler is providing.
    The distribution and heat emitters always drive the boilers operatuing condition. Good or bad.
    Delta T across S&R will, and should move during the transient period also. High load, cold start expect a wide ∆, closing as the room nears setpoint.
    Regardless if the design was 20, 25, 42, whatever, the heat emitters will drive that delta, up until equalibrium, it will move. Maybe at equalibrium condition the ∆ will match design. Maybe not :)
    It is at that thermal equilibrium condition you want to observe temperatures and deltas, with your camers or strap on temperature gauges. This confirms heat output, expectations, etc.
    On high mass, large system volume systems you want to observe the boiler return, assure it is adequate if you have a non condensing boiler.
    You would want that data on a design day ideally to assure you cracked the nut.
  • sre92
    sre92 Posts: 21
    I think it might make sense to keep the pump where it is for now until it gets colder and I can better assess if it is operating well when it is close to the design point. I didn't get anywhere near equilibrium with my test recently, since it isn't really cold out yet. If I see return temps dropping too much (I do have a non-condensing boiler) I'll get a pump that will actually make more flow, maybe something like the Alpha2 26-99, which I think could do in the range of 16-20GPM.
    If you do find the return is dropping below 130 for over a 10 minute period you would want a boiler protection valve or device, not a larger pump. The boiler needs a "thermal clutch" to allow it to keep up with the load of the system. The pump should move just enough gpm to get the job done, no need to over-pump.
    The graphic below shows how the valve monitors return temperature and blend boiler supply to maintain 130. The tank as a load is to show a big hungry load. Pellet and wood fired boilers are often connected to large buffer tanks. That is the most common application for return protection valves.
    Now if the boiler is oversized, taming short cycles gets trickier.