Multiple boiler piping
Few questions in regards to multiple boiler piping..
1st is about system circulator.. I included a quick drawing with 2 options for circulator location. Can anyone suggest the proper (or better) location for the system circulator ??
And this job is gonna have 3 boilers installed, obviously each with it's own circulator…
So question 2, is there a preference as to which side of the boiler each boiler circulator should be ? On supply or return of boiler?
And 3rd, does each individual boiler need a check valve in the piping ? Again, is it preferred on supply or return of boiler?
Thanks for any advice.
    hot_rod Posts: 28,704
    What type of boiler?
    What type of distribution?
    With conventional CI boilers, pumps could be on either Sor R
    With high pressure drop mod cons, pump into the turn.
    A hydraulic separator make for a nice installation, giving you air, dirt, mag, and hydraulic separation.
    If it is a high mass distribution, CI boiled may need return protection.
    Screenshot 2026-08-30 at 7.52.09 AM.png Screenshot 2026-08-30 at 7.47.55 AM.png
    Option 2 I like better regardless of the boiler as far as the system circ goes.
    As far as the boiler(s) circulators I would put them on the return if it is a mod con with a high pressure drop. CI boilers it probably doesn't matter.
  • gpjazz
    gpjazz Posts: 106
    They will be cast iron boilers
    The expansion on the inlet side of the boiler and system pump.
    Air purger at supply from boilers