Options
wvukidsdoc
wvukidsdoc Member Posts: 7

First off I am starting a new thread, hope that is OK here.

So many thanks last week to all who answered. As it ends up, I’m surprised that Google lens, and no one got this. I got to dad‘s yesterday, and of course he had the manuals from 30 years ago. It is a Watts Isotherm “control module” and after reading the summary below, I have a bit better understanding of what was intended and why I didn’t get it. Mostly, the three-way mixing valve here is running backwards with pilot flow, and as someone identified, the box with orange knob is an aquastat, however it actually was for HIGH temp protection, this thing does nothing for boiler return protection other than luck. Further the knobs on the isolation valves were correct because unknown to me dad”s zone valves are on his return manifold which leads to some issues in my mind since this things supply side manfold connects directly to the high temp return manifold.

IMG_1682.jpeg

So now for an as built which might explain why it never may have worked properly. In his defense dad installed it the way his 5 page manual described. But looking online at a spec sheet on a Hungarian site, it is stated that the supply and return are supposed to be onto a primary loop, with this a secondary loop. Pardon the poor sketch, but this is what is there largely. All major components shown. Of note there are no differential pressure reliefs between either manifold set. The remote expansion tank and air scoop are also on the outlet side of the system/boiler circulator. The Isotherm circulator does run only with it’s loops, the system/boiler circulator with any call for heat. Both pumps are Grundfoss 15-58 both set to middle speed. The system is full of rust and sludge but is 30 years old. I am replacing the boiler like for like, Utica/Dunkirk cast iron, power vented, the original was a Sears branded Dunkirk power vented.

IMG_1883.jpeg

The thermostatic mixing valve on the Isotherm is a rock. Even after soaking for two days in CLR, judicious application of heat and penetrating oil, it is a paperweight. I see that it is easily available in the UK for 144 quid, but it does not exist in the US. Further, the circulator is probably questionable and the piping between them is severely corroded anyway. Plus again I don’t know if this truly worked as built anyway. .I have 10 days and the following things here at my disposal that I have collected over the years.

2 Honeywell AM101R-US-1 mixing valves (Cv 3.9)

A Taco I Series-S in 3/4 sweat (Cv 3.4)

A couple Taco 3196-1 differential pressure valves

Lots of new Grundfoss 15-58 pumps and a Taco 007-f5

A Tekmar 362 (which does power on, and was good 20 years ago when I took it out of service)

3 thermistors that should work more or less for either the I Series or the 362.

Fos context, the low temp is 4 loops of 1/2 Pex, 150-250 ft per loop.

Absolutely ANY suggestions for mixing and boiler return protection with what I got MUCH appreciated. I would very much prefer to not mess with either manifold, or the zone valves, though I could reconfigure them a bit. I have plenty of 1 1/4, 1, and 3/4 copper, a good assortment of pump flanges, etc.

Finally, I really don’t want to use the Tekmar 362 unless absolutely necessary, as there is no guarantee it still works, and I would hate to blow three or four days trying to figure that out. If somebody tells me hands-down, it is the smart choice, I’m receptive to it, it just may doom me.

Comments

  • hot_rod
    hot_rod Member Posts: 28,057

    the rule of thumb is IF the low temperature zone is 10% or less of the boilers output, return protection is not really needed.

    Basically the boiler has enough capacity to raise the return when that zone runs

    Not knowing the total heat load compared to boiler output, I suspect you are fine

    Depending on how much upgrading you want to do!

    Id like to see the circ on the supply after the expansion tank

    Id rather the zone valves on supply to prevent ghost flow, but probably not worth changing it there have not been over heating zones?

    The HW am valve will work there are two piping options that still allow the radiant to run by itself, even if no hi temp zones are on.

    The wild loop is the simplest, use a real balance valve, not a ball valve, so you have fine tuning across the wild loop

    The additional zone valve , option 1 involves more wiring

    You fix isn’t really too complicated

    IMG_3096.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • wvukidsdoc
    wvukidsdoc Member Posts: 7

    Bob, I didn’t call out on the pic, just drew them, but there are 4 zone valves on the low temp supply manifold, so does my return need to go through the additional zone valve or just dump into the return manifold? Dad (retired EE) has a bunch of switch logic running the pumps appropriately as it stands. You figure the 3/4” sweat AM1 is OK for the 8 gpm max flow?


    I am a bit concerned about return as I downsized the boiler based on back calculating from his actual natural gas usage from a few worst months the last few years. I got a deal on a 112k, the prior had been 150k. I haven’t truly measured but back of envelope would suggest by sq ft living space could be right on the hairy edge, though it is mostly bare joist staple up so maybe better than I think.

    I will definitely move the boiler circulator, no problem there. I could relatively easily reverse the high temp manifolds in total but the air bleeds on baseboards will end up in some funky places, and the house hasn’t had problems.

    Should I put the differential pressure valves in anywhere?


    Thanks so much,

    John

  • JasonHogan
    JasonHogan Member Posts: 1

    For 4 loops of 1/2" PEX at 150–250 ft each (staple-up), your total low-temp radiant flow requirement is likely only 2.0 to 3.0 GPM max (roughly 0.5 to 0.75 GPM per loop for standard temperature delta), nowhere near 8 GPM.

    That means the Honeywell AM101R (Cv 3.9) will handle the radiant side easily without causing excessive pressure drop.

    Regarding your other questions:

    1. Differential Pressure Bypass: Since you have zone valves on the manifold and a multi-speed Grundfos 15-58, you usually don't need the Taco 3196 DP valves on the radiant manifold if the pump is sized correctly on low/medium speed, or if you ever swap it to an ECM pressure-sensing circulator (like a Taco 0015e3 / Grundfos Alpha). If you do stick with the fixed 15-58 and zone valves close dead-heading the pump, running the circulator on Speed 1 or having a small bypass loop is plenty.
    2. Boiler Return Protection on Downsized 112k: With staple-up radiant (which acts as a high-resistance, relatively low-output emitter compared to embedded concrete slab), the thermal mass is low. The cast iron boiler water volume will recover fast enough without condensing issues during steady state.
    3. Piping clean-up: Moving the boiler circulator to the supply side pumping away from the expansion tank point of no pressure change (PONPC) as Bob suggested will make the biggest improvement to air elimination and pump cavitation prevention.

    Skip reviving the 20-year-old Tekmar 362 — with a 10-day timeline, piping the Honeywell AM-1 as a secondary injection/mixing bridge will get your dad up and running with minimal fuss and zero controller headaches.