First time home buyer
sonicL
sonicL Member Posts: 2
Buying home with gas hot water heat. Flagged for burn through on inspector. Sellers HVAC person says immediate replacement not necessary that it remains “functional”
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,709
    More pictures please. Straight on that spot and all sides of boiler. Mad Dog
  • Ironman
    Ironman Member Posts: 7,940
    edited August 8
    The boiler needs to be inspected by a competent pro and the cause of the burn mark determined.
    It could be that the heat exchanger is dirty, the burners are dirty, chimney blockage, improper draft, or something else. At any rate, it should not be run as it could pose a carbon monoxide risk or fire hazard.
    I wouldn’t buy the house until it’s properly repaired or replaced and a combustion analysis is done to confirm it’s safe.
    Bob Boan
    sonicLMad Dog_2HVACNUT
    mattmia2 Member Posts: 17,819
    it could be many things, we'd need more information. it could be anything from insufficient combustion air to a failed boiler section. it could be parts of the burner are rusted out, it could be the boiler is sooted up, it could have problems with low water return temps. you need your own heating contractor to look at it and tell you what is wrong and what the fix is. where are you located, we may know someone.
    that is just a symptom of many of the possible causes and if they aren't fixed a new boiler will do the same thing. depending on what is happening it may be possible to fix the cause and fix that boiler too.
    did anyone in this process take the front cover off and look in the combustion chamber?
    sonicLMad Dog_2
  • sonicL
    Thank you so much for the comments. My son is buying the home in Providence. Over 100 years old. I’m out of State. I told him he needs to get his own HVAC guy in to inspect. These comments were very helpful….The home is under contract but some negotiation about findings on inspection. I live in a much less expensive area and have never owned an old home. The home is expensive and he will need to prioritize a number of needed repairs.
    if it has cast iron radiators and is a converted gravity system it could very likely be the effects of not having proper return water temp protection causing sustained condensation in the boiler. that could mean it is blocked with soot or rust or is rusted out.
    Steamhead Member Posts: 18,781
    Providence- the one in Rhode Island?
    (Some of us will know what song that line came from)
    Consulting
  • HydronicMike
    HydronicMike Member Posts: 404
    I wouldn’t trust the ‘buyers HVAC person’. They have no fiduciary responsibility to you unless they want to give you a written guarantee and extended warranty.
    IronmanMad Dog_2mattmia2
    EBEBRATT-Ed Member Posts: 20,755
    @sonicL
    The cause of the burn mark is probably due to dirty burners, dirty boiler or plugged chimney. It can most likely be fixed by the right technician but that is when the problem starts. Most hvac contractors will tell your son to replace the boiler because they are brought up to sell new equipment and can't be bothered to fix anything.
    The home inspector was right to call this out.
  • Mad Dog_2
    edited August 8
    Try to get Ryan from New England Steam Works in there. Rhode Island guy Based in Providence. Excellent. He can be found in The Find a Contractor feature in this site. Mad Dog
    Ironmanmattmia2