Boiler replacement.
luma
luma Member Posts: 20
Hello All,
My existing 5 zone Burnham Revolution boiler unfortunately start leaking and I’m planning on replacing it with a Weil-Mclain Evergreen EVG-155. My current setup is one zone a DHW, the rest are being controlled by Taco 555 Zone Valves. I had 3 different companies provide me with estimates and quotes do vary significantly, but obviously they are not really comparable since each company wanted to use different equipment. All of my zones are being controlled by Nest thermostats, neither has C wire nor would I be able to run a different cable to address a missing C wire. When a new boiler is installed, I’d like to install a Taco ZVC panel (I like the clean simplicity of this thing), the question I have is whether I should go with zone valves or circulating pumps. Currently I have a single pump, but for the past 2 and half years I’ve been replacing zone head valves like crazy. My understanding is that newer Taco Sentry Zone Valves don’t work well with Nest, so should I go with the older Taco valves I have or replace them with circulating pumps, thinking using Taco 007e circulating pumps. I know that this seems to be a rather old question, after all most of us have our own preferences, but what would your recommendation be?
Thank you
  • pedmec
    pedmec Member Posts: 1,460
    Why would the zone sentry be an issue with the nest thermostat? The thermostat is going to be wired into your ZVC. The issue you will have is that you need to use the resistors that come with the ZVC. If you install the resistors you should not have a problem. At least in my experience with the nest and the ZVC. Just install the resistor between W and C on each zone in the ZVC.
  • luma
    Thank you for the advise, will have to give it a try.
    EdTheHeaterMan Member Posts: 12,491
    Every circulator will add more Gallons Per Minute GPM flow to the system that probably does not need more GPM flow. If the circulator pump can handle the entire system when all the zones for heat call, then there is no reason to add more pumps.
    to turn this down to basic rule of thumb we often use in this trade: 1 GPM = 10,000 BTUh
    If you have a boiler that has a net output of 124,000 BTUh NET, then you need to move 12.4 GPM when the boiler is at full output capacity. Having 5 zones with 5 pumps is really overkill. Especially when one pump can handle 12.4 GPM with no problem, if needed. I believe Zone Valves are the way to go for you.
    And @pecmsg always has very helpful comments regarding Nest Thermostats. I applaud him for his convection on such a controversial topic.
    Alan (California Radiant) ForbesPeteAIntplm.
    hot_rod Member Posts: 27,806
    edited April 26
    I agree with Ed, a common residential circ, 1/12 hp, or ECM version can move 8, 10 or more gpm. That is plenty for common 100,000 btu or so.
    On multi zoned 100K systems, the circs may only be moving 1 gpm or so on small zones
    So a zone valve system with a variable speed ECM delta P circ, the flow adjusts as zones open snd close. Think of it as a cruise control for the distribution
    Add ODR to the boiler and now that too is on cruise control
    more on zoning
    https://www.caleffi.com/sites/default/files/media/file/Idronics%2036%20Final.pdf
    PeteAIntplm.
  • luma
    Thank you very much all for your feedback, much appreciated! I kind of agree with comments on Nest, but it is what it is. I truly hope that Taco ZVC will solve the issue.
  • SteveSan
    SteveSan Member Posts: 301
    There shouldn't be any issues wiring Nest to our ZVC controls. If you do need a resistor, our 1,000ohm 1/2watt won't work with Nest. They ( Nest ) suggest using a 220ohm and up to 5 watt. Our resistors should work with any other t-stat.
    EdTheHeaterManpecmsg
    mattmia2 Member Posts: 17,409
    perhaps the nest's parasitic current is what keeps cooking your heat motor taco zone valves
    pecmsg
    @hot_rod said: "Add ODR to the boiler and now that too is on cruise control"
    I believe the WM evergreen boilers come with the Outdoor Reset (ODR) feature included and are shipped with the outdoor sensor for that purpose.
  • pedmec
    @SteveSan i have successfully used the resistors that come with the ZVC but i could have sworn they were 600 watt resistors. as Roger Clemens once stated "was i misremembering".
    PeteA
    maybe 600 ohm. a 600 w resistor would be the size of a paint can.
    PeteA
  • pedmec
    @mattmia2 My bad lol
    mattmia2PeteA
  • luma
    @SteveSan, thank you for the advise. In my current setup, I do have two different central ACs, which are connected to 2 Nests. I've attempted to solve my missing C wire issue with Nest Power Connect, but I could not figure out how to install it for my particular situation. My understanding is that NPC would be a better option than a resistor if I'll figure out how to connect it.
  • SteveSan
    @luma I would wire in the NPC first and adding the resistor should be the last option.
  • luma
    Sounds like a plan, thank you again.
    SteveSan
